Posted: 2020-07-05 05:43 PM
This answer was originally posted on DCIM Support by Steven Marchetti on 2019-03-05
Hi Michael,
Single phase Easy-UPS use the generic SNMP UPS mib and would easily be monitor-able by either DCE or NetBotz with a 5 node monitoring pack. I would suggest using DCE as you can provide more resources and that is it's main purpose.
The 3 phase units have their own MIB. DCE by default does not have a DDF added to the system for this UPS. You would want to use the DDF menu at the top of the page to request a DDF for it. As for the NetBotz appliances, I do not believe DDFs are being actively created for the NetBotz so if that is indeed the case, you wouldn't be able to monitor it using the 570.
Thanks,
Steve.
(CID:140710957)
Posted: 2020-07-05 05:43 PM
This comment was originally posted on DCIM Support by spezialist on 2019-04-01
Dear Michael Ng,
Tell us, please, did you solve your question or not?
With respect.
(CID:141269243)
Posted: 2020-07-05 05:43 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.