Can NBPD0150 and NBPD0170 be daisy chained off of the same NBRK0570? If so, how often would an additional power supply be needed and where?

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
DCIM_Support
Picard
Picard
0 Likes
2
206

Can NBPD0150 and NBPD0170 be daisy chained off of the same NBRK0570? If so, how often would an additional power supply be needed and where?

This question was originally posted on DCIM Support by douglas.ulrich on 2016-08-24


Can NBPD0150 and NBPD0170 be daisy chained off of the same NBRK0570?

If so, how often would an additional power supply be needed and where?

Such as:

570 > [170 > 150] > [170 > 150 ] > [170 > 150] > etc.

We are thinking about a design that involves a 170 and 150 on each rack, for door/card access sensors and temp/humid sensors respectively.

(CID:108234832)


Accepted Solutions
DCIM_Support
Picard
Picard
0 Likes
0
206

Re: Can NBPD0150 and NBPD0170 be daisy chained off of the same NBRK0570? If so, how often would an additional power supply be needed and where?

This answer was originally posted on DCIM Support by Cory McDonald on 2016-08-24


Douglas,

Mixing sensors pods and rack access pods can make it difficult to judge where to add external power supplies.  The users guide recommends adding one every 10 sensor pods or 4 rack access pods.  My recommendation would be to add one every 3 racks (3 150s and 3 170s).  If power issues with PODs disconnection and reconnecting occur, additional power supplies would need to be added.  So the setup would look like this:

570 > [170 > 150] > [170 > 150 ] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > 170(external power).

Please keep in mind that the NetBotz 570 only support 12 sensor pods and 13 rack access pods.

If you are not looking to add more than a few sensors per rack, you could run a 150 only every few racks and then just run the sensors to the racks next to the rack that has the 150.

Regards,

Cory

(CID:108234834)

See Answer In Context

2 Replies 2
DCIM_Support
Picard
Picard
0 Likes
0
207

Re: Can NBPD0150 and NBPD0170 be daisy chained off of the same NBRK0570? If so, how often would an additional power supply be needed and where?

This answer was originally posted on DCIM Support by Cory McDonald on 2016-08-24


Douglas,

Mixing sensors pods and rack access pods can make it difficult to judge where to add external power supplies.  The users guide recommends adding one every 10 sensor pods or 4 rack access pods.  My recommendation would be to add one every 3 racks (3 150s and 3 170s).  If power issues with PODs disconnection and reconnecting occur, additional power supplies would need to be added.  So the setup would look like this:

570 > [170 > 150] > [170 > 150 ] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > 170(external power).

Please keep in mind that the NetBotz 570 only support 12 sensor pods and 13 rack access pods.

If you are not looking to add more than a few sensors per rack, you could run a 150 only every few racks and then just run the sensors to the racks next to the rack that has the 150.

Regards,

Cory

(CID:108234834)

DCIM_Support