EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:23 AM . Last Modified: 2024-04-08 11:21 PM
Can NBPD0150 and NBPD0170 be daisy chained off of the same NBRK0570?
If so, how often would an additional power supply be needed and where?
Such as:
570 > [170 > 150] > [170 > 150 ] > [170 > 150] > etc.
We are thinking about a design that involves a 170 and 150 on each rack, for door/card access sensors and temp/humid sensors respectively.
(CID:108234832)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:23 AM . Last Modified: 2024-04-08 11:21 PM
Douglas,
Mixing sensors pods and rack access pods can make it difficult to judge where to add external power supplies. The users guide recommends adding one every 10 sensor pods or 4 rack access pods. My recommendation would be to add one every 3 racks (3 150s and 3 170s). If power issues with PODs disconnection and reconnecting occur, additional power supplies would need to be added. So the setup would look like this:
570 > [170 > 150] > [170 > 150 ] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > 170(external power).
Please keep in mind that the NetBotz 570 only support 12 sensor pods and 13 rack access pods.
If you are not looking to add more than a few sensors per rack, you could run a 150 only every few racks and then just run the sensors to the racks next to the rack that has the 150.
Regards,
Cory
(CID:108234834)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:23 AM . Last Modified: 2024-04-08 11:21 PM
Douglas,
Mixing sensors pods and rack access pods can make it difficult to judge where to add external power supplies. The users guide recommends adding one every 10 sensor pods or 4 rack access pods. My recommendation would be to add one every 3 racks (3 150s and 3 170s). If power issues with PODs disconnection and reconnecting occur, additional power supplies would need to be added. So the setup would look like this:
570 > [170 > 150] > [170 > 150 ] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > [170(external power) > 150] > [170 > 150] > [170 > 150 ] > 170(external power).
Please keep in mind that the NetBotz 570 only support 12 sensor pods and 13 rack access pods.
If you are not looking to add more than a few sensors per rack, you could run a 150 only every few racks and then just run the sensors to the racks next to the rack that has the 150.
Regards,
Cory
(CID:108234834)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:23 AM . Last Modified: 2023-10-31 10:18 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.