Can DCE control AP8953 What they use A-Link connection well?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Can DCE control AP8953 What they use A-Link connection well?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:56 PM . Last Modified: ‎2024-04-03 12:18 AM

0 Likes
3
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:56 PM . Last Modified: ‎2024-04-03 12:18 AM

Can DCE control AP8953 What they use A-Link connection well?

Hi

My customer want to use Swithed PDU (AP8953) With A-Link (Port Sharing )

Because they want to reduce assigned ip address and network cables

And also they want do individual port control by DCE

If they configure port sharing with AP8953 and also they do output port control by DCE

will it working well without problem ?


(CID:150241358)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:56 PM . Last Modified: ‎2024-04-03 12:18 AM

0 Likes
1
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:56 PM . Last Modified: ‎2024-04-03 12:18 AM

Dear Doody,

Please check this k-base document

https://www.se.com/us/en/faqs/FA239801/

 

Issue:

StruxureWare Data Center Expert does not support APC rPDUs using network port sharing.

Product Line:

InfraStruxure Central
StruxureWare Data Center Expert
AP8xxx APC rack mount PDU2

Environment:

StruxureWare Data Center Expert 7.x and earlier
AP8xxx APC rack mount rPDU2 using network port sharing

Cause:

When using network port sharing, the SNMP output of the rack mount PDU is not seen by StruxureWare Data Center Expert in a format that can properly associate the different outlets with their respective PDUs.

Resolution:

The current resolution is to not use the network port sharing and add each rPDU individually by it's own IP. A future revision of StruxureWare with the ability to properly associate the outlets with their respective PDUs when using the network port sharing feature is being looked at but there are no firm dates or versions at this time.
 

(CID:150241373)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:56 PM . Last Modified: ‎2024-04-03 12:18 AM

0 Likes
1
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:56 PM . Last Modified: ‎2024-04-03 12:18 AM

Dear Doody,

Please check this k-base document

https://www.se.com/us/en/faqs/FA239801/

 

Issue:

StruxureWare Data Center Expert does not support APC rPDUs using network port sharing.

Product Line:

InfraStruxure Central
StruxureWare Data Center Expert
AP8xxx APC rack mount PDU2

Environment:

StruxureWare Data Center Expert 7.x and earlier
AP8xxx APC rack mount rPDU2 using network port sharing

Cause:

When using network port sharing, the SNMP output of the rack mount PDU is not seen by StruxureWare Data Center Expert in a format that can properly associate the different outlets with their respective PDUs.

Resolution:

The current resolution is to not use the network port sharing and add each rPDU individually by it's own IP. A future revision of StruxureWare with the ability to properly associate the outlets with their respective PDUs when using the network port sharing feature is being looked at but there are no firm dates or versions at this time.
 

(CID:150241373)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:56 PM . Last Modified: ‎2024-04-03 12:18 AM

In response to DCIM_Support
0 Likes
0
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:56 PM . Last Modified: ‎2024-04-03 12:18 AM

Dear Balaraman Jagadeesan and Doody.choi,

Pay attention to the date above the specified k-base document, it is outdated:

For about five years now, I have been successfully using a huge number of rPDUs AP8881 and AP8853, for example, in Network Port Sharing mode with DCE software.

This of course does not apply to switched outlet rPDU (I do not have such). But a lot of time has already passed from the date above the indicated k-base document and several versions of DCE software and the corresponding ddf-files have changed. It seems to me, that you first need to try and check whether the latest version of DCE-7.7.1 will work normally with switched outlet rPDU in Network Port Sharing mode.

If you have additional questions, please ask.

With respect.

(CID:150241593)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:56 PM . Last Modified: ‎2023-10-20 05:04 AM

0 Likes
0
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:56 PM . Last Modified: ‎2023-10-20 05:04 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of