Becon/Siren Alarm in DCE

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

DCIM_Support
Picard
Picard
0 Likes
2
192

Becon/Siren Alarm in DCE

This question was originally posted on DCIM Support by Momen Samy on 2017-11-13


Hi,

Kindly i have a customer that need a solution for activating a Becon/Siren in the case of any "Critical" category Alarms from DCE.

Project Details as below;

  • DCE V7.4.3
  • We have 23 NetBotz 570 appliances connected to the DCIM system.
  • We have different types of devices with different protocols connected to the DCIM system, as follows;
    1)  3 UniFlair units >> SNMP over TCP/IP
    2) 44 CRAC units >> SNMP over TCP/IP
    3) 4 UPS >> SNMP over TCP/IP
    4) 3 Generators >> ModBus/Serial, and connected to the DCIM switch through a Gateway (Serial to Ethernet).
    5) 14 Power Meters >> ModBus/Serial, and connected to the DCIM switch through a Gateway (Serial to Ethernet).

(any "Critical" Category alarm from these devices must initiate a Becon/Siren)

 

I've tried another solution >> PC connected to high volume speaker to get sound notification whenever there is an alarm in the devices, as below;

 Unfortunately, the drawback of this way is that the Alarm sound will not differentiate the Critical Alarm category (i.e: sound will play in case of any alarm), also, the sound will be played once (while we need it to be played continuously until the Alarm is cleared).

 

BR

(CID:126175739)

2 Replies 2
DCIM_Support
Picard
Picard
0 Likes
0
192

Re: Becon/Siren Alarm in DCE

This answer was originally posted on DCIM Support by Steven Marchetti on 2017-11-13


Hi Momen Samy,

DCE has only that one option to play a sound and the client must be running on a computer for the sound to be heard. There is sadly no alternative configuration for this option. 

I can add this as an enhancement request (you can too under the resources menu) however I can't say when the feature will make it into the system if at all.

 

 

Steve

(CID:126175915)

DCIM_Support
Picard
Picard
0 Likes
0
192

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.