Beacon disconnected alarm when uploading ini file to PX-HID AP9361

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Beacon disconnected alarm when uploading ini file to PX-HID AP9361
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:35 AM

0 Likes
9
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:35 AM

Beacon disconnected alarm when uploading ini file to PX-HID AP9361

Not sure if you are aware of this bug, but if you upload a config.ini file to the PX-HID controller in order to change the User Access configuration, then there is a chance it will make the PX-HID show the alarm "Beacon disconnected" afterwards, which also shows up on DCE.

I uploaded the config.ini files to approx 30x PX-HID using the APC ini upload utility and out of those around 12x came up with this alarm.

The only way I could remove this alert was to physically log in to every PX-HID that was in alarm condition and manually reset the "Lost Communications Alarms". Painful...

None of them have beacons connected.

 

(CID:126163094)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:35 AM

0 Likes
7
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:35 AM

Hi Garry,

 

I've seen that issue on startup but I can't say I've seen it with a config.ini upload.

Do you know of any difference between the 18 that did not have the alarm and the 12 that did? 

Were they running different firmware?

Did you send a different config.ini to the ones that had the issue vs the ones that did not.

Could I get a copy / example of the config.ini you're uploading to the failed units?


Steve.

(CID:126163175)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:35 AM

In response to DCIM_Support
0 Likes
0
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:35 AM

Some are on 3.5.3 and some are on 3.9.1, but there did not appear to be a relationship between the FW revision and which ones showed the alarm.

I uploaded 5 different configuration files, but again there wasn't a relationship between the contents of the ini files and which devices showed the alarm.

I don't really want to post the other ini files here, but this one caused some of the alarms to appear.

HIDRemoveAll.ini

(CID:126163224)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:34 AM

In response to DCIM_Support
0 Likes
0
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:34 AM

Thanks Garry,

If this is all you did (add or remove users) and included no other sections (what I was most concerned with), this one is enough. Actually adding data shouldn't matter at that point. Did you actually delete users then re-add them to all devices? If so, how long between the ini pushes? I'm wondering if that could have any effect.

I'll try to replicate but I don't have a large number of units to test so it'll be pushing to one unit over and over.

 

Steve

(CID:126163247)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:34 AM

In response to DCIM_Support
0 Likes
0
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:34 AM

I have had occasions in the past where pushing the users to the HID without first deleting all users first doesn't always work.  Some users get updated and some don't.

Based on this, I first deleted all users from all racks, then pushed different ini files to each 'batch' of racks.  I would say 3-5 minutes between pushes. (I checked the event log on one of the devices to check the users had been deleted, before pushing the next ini file)

The Beacon disconnected alarms do occur when using the ini file I supplied.

 

Also to confirm, the 'Beacon Disconnected' alert is not new (to me), but I have never gotten round to posting it here before.

 

(CID:126163286)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:34 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:34 AM

Thanks,

Yes, you should always delete them first. I just wasn't sure if you were changing them, just adding them, etc. Just trying to get as much info for testing as possible.

 

Steve

(CID:126163292)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:34 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:34 AM

Hi Garry,

 

I just wanted to let you know that I haven't been able to replicate your issue. I got a config file from an AP9361 and whittled it down to just the users. I put  the removeall.ini a dozen times then intermittently pushed the removeall and the config.ini multiple times. I tried this through ftp as well as through the ini utility. I tried manually entering the info as well as using the text file list to add them. 

If you're doing anything specific, let me know, I will try and test a few more times when I get the chance and I will let the engineers know you've seen this but if I can't replicate, I'm not sure what more I can do. I'll try to get another unit too...just in case.

Steve.

(CID:126163300)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:34 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:27 AM . Last Modified: ‎2024-04-05 04:34 AM

Just wanted to let you know, I spoke to one of the engineers and they have seen this in the past but were unable to connect it with any specific ini change. They're going to look at it again.

 

Steve

(CID:126163353)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:28 AM . Last Modified: ‎2024-04-05 04:34 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:28 AM . Last Modified: ‎2024-04-05 04:34 AM

Hi Garry,

 

Sorry it's been so long but engineering had looked into this but they don't have a good prognosis. The AP9361 is going end of life and as such, they're not looking into re-writing any firmware going forward (except possibly extreme security issues should they arise).

What they had suggested was that the device may have had the beacon or something connected to that port (maybe just during initial inspection) and somehow held on to that variable.  They suggested trying to disconnect all sensors and resetting the device to defaults to see if that clears anything. 

Do you have an idea on the age of these units? 

 

Steve

(CID:126884874)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:28 AM . Last Modified: ‎2023-10-20 05:03 AM

0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:28 AM . Last Modified: ‎2023-10-20 05:03 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore