Battery near end of life

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Battery near end of life
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:29 AM . Last Modified: ‎2024-04-05 03:18 AM

0 Likes
5
18860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:29 AM . Last Modified: ‎2024-04-05 03:18 AM

Battery near end of life

We are getting warnings that our batteries on our 10 kVa UPS's are near end of life.  They are only 2.5 years old.  I don't mind the reminder but at a age I would like to set for myself.  Where can I set this threshold.  My alternative is to just disable the Alarm Configuration "Battery Near End Of Life" but I would rather not.

(CID:128059664)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:29 AM . Last Modified: ‎2024-04-05 03:18 AM

In response to DCIM_Support
0 Likes
0
18844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:29 AM . Last Modified: ‎2024-04-05 03:18 AM

Hi Michael,

 

Log into the UPS directly. Go to Configuration–> UPS. You should see the following configuration options (I've got slightly older firmware on my SRT 10k but it should be similar):

Please note that the battery warning max (at least as I see it) is maxed out at 730 days. There is also an acknowledgement sleep time so once acknowledged, it should wait a while to come back. This is so you can proactively configure warnings to know when you should think about changing the battery. You can change this or even disable this and the device will still alarm when the battery is bad.


Steve

(CID:128061445)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:29 AM . Last Modified: ‎2024-04-05 03:18 AM

0 Likes
3
18844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:29 AM . Last Modified: ‎2024-04-05 03:18 AM

Hi Michael,

What UPS is it? Is it an APC ups and I so, which and with what firmware?  Did someone create a threshold for the battery? Is the device itself reporting the battery being old? 

 

Steve 

 

(CID:128059802)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:29 AM . Last Modified: ‎2024-04-05 03:18 AM

In response to DCIM_Support
0 Likes
0
18844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:29 AM . Last Modified: ‎2024-04-05 03:18 AM

This is a 10 kVa UPS Model Smart-UPS SRT 10000 running v6.4.6 and the device alarm is under Battery/Battery Near End Of Life.  My only option is to either replace the battery or disable the Device Alarm Configuration for that point.  Is there a way to set a longer time before that alarm appears as a reminder because that is what that is doing, reminding you of the age of the battery.  There has been no failure and the battery is passing tests.

Thanks...

(CID:128061438)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:29 AM . Last Modified: ‎2024-04-05 03:18 AM

In response to DCIM_Support
0 Likes
0
18845
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:29 AM . Last Modified: ‎2024-04-05 03:18 AM

Hi Michael,

 

Log into the UPS directly. Go to Configuration–> UPS. You should see the following configuration options (I've got slightly older firmware on my SRT 10k but it should be similar):

Please note that the battery warning max (at least as I see it) is maxed out at 730 days. There is also an acknowledgement sleep time so once acknowledged, it should wait a while to come back. This is so you can proactively configure warnings to know when you should think about changing the battery. You can change this or even disable this and the device will still alarm when the battery is bad.


Steve

(CID:128061445)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:30 AM . Last Modified: ‎2024-04-05 03:18 AM

In response to DCIM_Support
0 Likes
0
18844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:30 AM . Last Modified: ‎2024-04-05 03:18 AM

P.S., there is another option that is not editable. Under UPS status, there is:

Next Battery Replacement Date.
On mine it is:
03/26/2022
This is not editable. 
If you receive this alarm, you can either:
1, replace the battery
2, disable the alarm.

Steve

(CID:128061447)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:30 AM . Last Modified: ‎2023-10-20 05:03 AM

0 Likes
0
18844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:30 AM . Last Modified: ‎2023-10-20 05:03 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore