BCPM with DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • BCPM with DCE
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:40 PM . Last Modified: ‎2024-04-09 03:04 AM

0 Likes
8
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:40 PM . Last Modified: ‎2024-04-09 03:04 AM

BCPM with DCE

Anyone has some experience to integrate BCPM in DCE?

There is a best practice guide to do it?

Regards,

 

Enric Climent

(CID:102924943)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:40 PM . Last Modified: ‎2024-04-09 03:04 AM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:40 PM . Last Modified: ‎2024-04-09 03:04 AM

Hi Enric, Sorry, I am unfamiliar with BCPM. I tried looking it up and I come up with a dozen things from Benchmark Cost Proxy Model to Business Control and Process Management but none of what I find seems to fit this conversation. If you have a specific product or product page to which you could refer, that may make things easier. Likewise, if anyone else reading this thread has any ideas, I'll be more than happy to delete this comment. 😃 Steve

(CID:102924952)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:40 PM . Last Modified: ‎2024-04-09 03:04 AM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:40 PM . Last Modified: ‎2024-04-09 03:04 AM

Hi Steven,

Thanks for your interest. BCPM is a PowerLogic (Schneider) product that means Branch Circuit Power Meter.

Best regards,

 

Enric Climent

 

(CID:102925007)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:40 PM . Last Modified: ‎2024-04-09 03:04 AM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:40 PM . Last Modified: ‎2024-04-09 03:04 AM

Thanks Enric,

 

I've heard of the branch monitor, just not that specific acronym, sorry. I don't know that there is a best practices guide but as long as the system is set up to output modbus or SNMP, DCE can monitor it. You may need to get a DDF for the device before installing as I don't know that there is one on the system by default but here is a list of powerlogic DDF files that are available for Modbus by default.

To get DDFs for anything not already on the system or avialable in the add/update feature of the device definition files dialog box in DCE, you would want to contact  the folllowing group:

multivendorsupport@apcc.com

This group creates and maintains all the DDF files for both APC and non-APC devices. If during disco...

 

Thanks,

Steve.

(CID:102924970)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:40 PM . Last Modified: ‎2024-04-09 03:04 AM

0 Likes
2
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:40 PM . Last Modified: ‎2024-04-09 03:04 AM

Enric, BCPM has Modbus RTU output. I believe if we connect to TSXETG100 modbus gateway to modbus tcp, it shouldn't be a problem to have DCE to monitor it. Just get the modbus list, according to how many branch circuit for the BCPM (21*x), and send to multivendor support, they should able to create a DDF for you Regards. Law

(CID:102925009)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:41 PM . Last Modified: ‎2024-04-09 03:04 AM

In response to DCIM_Support
0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:41 PM . Last Modified: ‎2024-04-09 03:04 AM

Correct. I have already done this for a customer. the BCMP is a component of the BMS chain. Use eiether a TSXETG100 Ethernet Gateway, and configure this to gain information from the BCMP. My customer only had a ETG300, which had a ModbusTCP interface. We connected to the gateway, configured which slave id to present information via the thin client, then used DCE with a modbus device type, with an appropriate Modbus DDF.

(CID:102925010)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:41 PM . Last Modified: ‎2024-04-09 03:04 AM

In response to DCIM_Support
0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:41 PM . Last Modified: ‎2024-04-09 03:04 AM

Hi Warren, I'm designing a DCIM solution with many BCPMs (plus EGX100) to monitor circuit breakers. Can you confirm that the integration with the DCE has done successfully? Did you see correctly all the BCPM parameters? Thanks in advance. I would like to avoid to introduce a component with high risk during the integration phase. Roberto

(CID:104174417)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:41 PM . Last Modified: ‎2024-04-09 03:04 AM

0 Likes
0
706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:41 PM . Last Modified: ‎2024-04-09 03:04 AM

Hello Enric, We used a product called EnerSure, from TrendPoint (www.trendpoint.com/branch-circuit-monitoring/enersure/).

They are a Schneider partner and there is an existing DDF already made for it.

Works brilliantly and we will be soon rolling it out to more switchboards.

If you want to know more, let me know.

Craig

 

(CID:102925003)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:41 PM . Last Modified: ‎2023-10-31 10:17 PM

0 Likes
0
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:41 PM . Last Modified: ‎2023-10-31 10:17 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of