Hi,
We have DCE v7.2.1 and I am in the process of using SOAP to integrate DCE alarms into SCOM 2012.
I noticed today while testing that even though our NetBotz and DCE are set to Australia and hence celsius, alarms that are raised report fahrenheit in the description field when accessed via SOAP.
The alarm description within the DCE client shows celsius but the same alarm has fahrenheit when accessed via SOAP.
The Server Locale setting under Time Settings in Server Administration Settings in DCE is set to English (METRIC).
Is this a limitation of web services or is there somewhere I need to set something?
Thanks,
Steve
(CID:108234969)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:28 AM . Last Modified: 2024-04-08 11:20 PM
Further investigation today has allowed me to discover that there is a difference between how SoapUI talks to DCE and how PowerShell does it. Even though SoapUI shows Australia for the user setting under Help - System Properties, I have to set en-AU for the locale in the SOAP request. PowerShell on the other hand is retrieving the correct data without needing to set any value for the locale.
This means everything is working correctly within my scripts. I'll just need to set the locale when doing testing using SoapUI.
(CID:108235061)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:28 AM . Last Modified: 2024-04-08 11:20 PM
Further investigation today has allowed me to discover that there is a difference between how SoapUI talks to DCE and how PowerShell does it. Even though SoapUI shows Australia for the user setting under Help - System Properties, I have to set en-AU for the locale in the SOAP request. PowerShell on the other hand is retrieving the correct data without needing to set any value for the locale.
This means everything is working correctly within my scripts. I'll just need to set the locale when doing testing using SoapUI.
(CID:108235061)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:28 AM . Last Modified: 2023-10-31 10:14 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.