Alarms from Netbotz 250 not being seen / triggered immediately in DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Alarms from Netbotz 250 not being seen / triggered immediately in DCE
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:53 PM . Last Modified: ‎2024-04-04 03:31 AM

0 Likes
5
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:53 PM . Last Modified: ‎2024-04-04 03:31 AM

Alarms from Netbotz 250 not being seen / triggered immediately in DCE

Hello,

We have a number of Netbotz 250 devices that we are monitoring with DCE via SNMPv3.

According to what we have read, DCE configures the Netbotz 250 with a hidden trap receiver destination (priority scanning) so that alarms that are generated on the Netbotz send a trap immediately to DCE and then it is supposed to scan the Netbotz for the alarm information and take action accordingly.

We can see in our logs that the Netbotz 250's are sending these traps to the DCE but it is not alerting or indicating that an alarm has occurred.

Example:

Door sensor open/close - if there are multiple open / close alarms these generate a trap to the DCE for each instance however it shows nothing in its alarm history

We also have the DCE setup to poll the devices every minute and occasionally it will pick up a door alarm if it has occurred and is active at the same time as the poll.

However this is not ideal as we are relying on DCE to perform the monitoring and alerting and to keep a history of all the alarms that have occurred.

When the trap is sent from the Netbotz to DCE is this supposed to generate the alarm immediately or does that only occur if the alarm is still active when DCE scans the netbotz after the trap is received ?

The Netbotz 450 devices we have monitored via DCE never miss an alarm and all alerts are recorded by DCE.

Just trying to understand if this is expected for APC SNMP monitored devices or if something is not configured / working correctly.

Thanks,

 

Steve

(CID:133372955)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:53 PM . Last Modified: ‎2024-04-04 03:31 AM

0 Likes
3
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:53 PM . Last Modified: ‎2024-04-04 03:31 AM

Hi Steve,

 

The priority scanning option is the hidden trap receiver process to which you're referring. As long as it is set up properly, your 250 goes into alert and sends a trap. DCE does nothing with this trap other than puts that device next to be scanned. This is to rule out any potential false alarms.

When DCE then polls the device, it polls a specific alarm OID and if there is information available, it reads the data then based on the configuration both in the DDF that gets downloaded from the APC device (creates the device alarm info in DCE) and your configuration on that page, it alerts or doesn't.

If the event happens so quickly that the device sends a trap but the poll does not see any data in the alarm OID, it will not alert. If on the other hand, you've blocked the write community string on the device / network / firewall, or if you've not configured priority scanning, the device will not be scanned until it's next scheduled poll. This could take anywhere from a few seconds up to (if using defaults) 5 minutes. 

 

Thanks,

Steve

 

 

(CID:133372960)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:53 PM . Last Modified: ‎2024-04-04 03:31 AM

0 Likes
3
1142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:53 PM . Last Modified: ‎2024-04-04 03:31 AM

Hi Steve,

 

The priority scanning option is the hidden trap receiver process to which you're referring. As long as it is set up properly, your 250 goes into alert and sends a trap. DCE does nothing with this trap other than puts that device next to be scanned. This is to rule out any potential false alarms.

When DCE then polls the device, it polls a specific alarm OID and if there is information available, it reads the data then based on the configuration both in the DDF that gets downloaded from the APC device (creates the device alarm info in DCE) and your configuration on that page, it alerts or doesn't.

If the event happens so quickly that the device sends a trap but the poll does not see any data in the alarm OID, it will not alert. If on the other hand, you've blocked the write community string on the device / network / firewall, or if you've not configured priority scanning, the device will not be scanned until it's next scheduled poll. This could take anywhere from a few seconds up to (if using defaults) 5 minutes. 

 

Thanks,

Steve

 

 

(CID:133372960)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:53 PM . Last Modified: ‎2024-04-04 03:31 AM

In response to DCIM_Support
0 Likes
0
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:53 PM . Last Modified: ‎2024-04-04 03:31 AM

Thanks for the quick reply.

That is what I thought was happening.

Not ideal for door sensors which can trigger / clear very quickly.

Ok for smoke/water/temp and other "slow moving" sensors.

At least we know it is working as designed.

Thanks for your help.

(CID:133372968)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:53 PM . Last Modified: ‎2024-04-04 03:31 AM

In response to DCIM_Support
0 Likes
0
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:53 PM . Last Modified: ‎2024-04-04 03:31 AM

No problem. Just an FYI about the 450 though, they work totally different. They do all their own alerting and then just store the alert on DCE pushing it using http or https. 

(CID:133372974)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:54 PM . Last Modified: ‎2024-04-04 03:31 AM

In response to DCIM_Support
0 Likes
0
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:54 PM . Last Modified: ‎2024-04-04 03:31 AM

Thanks, realize that now about the 450.

In retrospect we should have standardized on all 450's instead of a mix of 450's and 250's.

(CID:133372982)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:54 PM . Last Modified: ‎2023-10-20 05:00 AM

0 Likes
0
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:54 PM . Last Modified: ‎2023-10-20 05:00 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of