After upgrade to DCE 7.4.3 sensor status stay at failure even though sensor returned to normal. Device keep showing link status"OFFLINE". No problem in previous version 7.3.x or 7.4.1

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • After upgrade to DCE 7.4.3 sensor status stay at failure even though sensor returned to normal. Device keep showing link stat...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:13 PM . Last Modified: ‎2024-04-07 11:56 PM

0 Likes
7
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:13 PM . Last Modified: ‎2024-04-07 11:56 PM

After upgrade to DCE 7.4.3 sensor status stay at failure even though sensor returned to normal. Device keep showing link status"OFFLINE". No problem in previous version 7.3.x or 7.4.1

(CID:122692506)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

0 Likes
5
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

Hi Jimmy Leung,

Without going into details: if the upgrade to DCE-7.4.3 was unsuccessful, you were able to restore the normal operation of your DCE-server from the backup (I hope you did it)?

Q: During the upgrade to DCE-7.4.3, you patiently waited for the end of the data migration as indicated in Update an existing DCE server:

IMPORTANT: The Data Center Expert v7.4.3 update performs a data migration that can take up to an hour to complete. Do not reboot the server during the update.

With respect.

(CID:122693581)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

In response to DCIM_Support
0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

Hi Spezialist,

Thanks for your feedback.
The upgrade was successful. I doubt whether this is a bug. I tried to re-scan the device, no change in device status. However, if i deleted the device from DCE and add the device back again, it is become normal immediately and can display sensors value correctly. Can you see where the problem might be?
Regards

(CID:122693585)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

In response to DCIM_Support
0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

It is very difficult to assume something, but still it looks like an incorrect data migration of the devices.

Please specify the complete list of devices (model) with which this problem occurred. Or this problem has occurred absolutely with all the devices on the DCE-server (even virtual devices)?

With respect.

(CID:122693595)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

In response to DCIM_Support
0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

This problem only affected about 25% of the devices. All the devices on DCE are using Modbus to request register reading from devices which include power meters and temperature/humidity sensors. The other 75% devices are reading the devices correctly which suggest the data migration during upgrade does not cause any problem on them.

Hope this help.

(CID:122693597)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

In response to DCIM_Support
0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

Jimmy Leung, this is very strange, since I did not have such problems when migrating 3d party Modbus TCP/IP devices.

Q1: After upgrading to DCE-7.4.3, have you checked the correctness of the DDF-file versions for Modbus TCP/IP devices (especially for 3d party devices)?

Q2: After upgrading to DCE-7.4.3, did you check the correctness of the polling settings (IP address, Slave ID, used DDF-file, timings) of Modbus TCP/IP devices (especially for 3d party devices)?

With respect.

(CID:122693593)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

In response to DCIM_Support
0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2024-04-07 11:56 PM

Hi all,

Some ddf files that can be loaded in DCE version 7.2.3 or 7.3.1 cannot be loaded in 7.4.3. Doing some tests, I'm wondering if 7.4.3 accept only a limited number of StateSensor values ? (I'm unable to load more than 16 StateSensor in a DDF files  into 7.4.3 and it's possible in previous versions). In your case, for a DDF file already loaded, that could explain that some StateSensor states are no more correctly returned.

Regards

(CID:124521848)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2023-10-20 04:59 AM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:14 PM . Last Modified: ‎2023-10-20 04:59 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore