hi, it is posible to extend the cable length of a AP9335TH sensor?
(CID:122692438)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:13 PM . Last Modified: 2024-04-07 11:56 PM
Hi Sergio,
As per k-base FA156085, you can extend the cable 50 feet...up to 100 on a NetBotz appliance.
Steve
(CID:122692442)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:13 PM . Last Modified: 2024-04-07 11:56 PM
Hi Sergio,
I just noticed a few differences in the manuals for different devices. Th distances may differ depending on the device to which you are connecting so be sure to check the manual for the specific device.
Steve
(CID:122692465)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:13 PM . Last Modified: 2024-04-07 11:56 PM
Dear Sergio,
Yes, it is possible to extend the length of this sensor by using CAT-5 straight cable.

Regards,
Bala
(CID:122692449)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:13 PM . Last Modified: 2024-04-07 11:56 PM
Thanks Steven and Bala.
We will use these parameters in the installation of the devices.
(CID:122693599)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:13 PM . Last Modified: 2023-10-20 04:55 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.