Is it possible? i have a NPS Server running and it works well, full admin on the boxes, However i want to deploy to my 200 UPS's rather than configuring the strings on each UPS, can this bee done under the deploy template?
Gary
(CID:106203818)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:40 AM . Last Modified: β2024-04-09 12:13 AM
Hi, Gary!
Yes it's possible to deploy this to your devices with DCE's mass configuration feature. But it's not possible to save your settings as template due to security reasons.
So you will need to enter secret each time you will deploy your configuration.
(CID:106203823)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:41 AM . Last Modified: β2024-04-09 12:12 AM
How do i add the secret when deploying a template?
(CID:106203847)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:41 AM . Last Modified: β2024-04-09 12:12 AM
Hi Gary! I've checked once again and it seems that RADIUS secret cant be configured via mass configuration. I got wrong with SNMP and users settings. Sorry for inconvience.
(CID:106203879)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:41 AM . Last Modified: β2023-10-31 10:13 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.