ATS - do I have to unplug the unloaded power cord to do a FW up grade

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • ATS - do I have to unplug the unloaded power cord to do a FW up grade
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
128
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:12 PM . Last Modified: ‎2024-04-07 11:10 PM

0 Likes
9
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:12 PM . Last Modified: ‎2024-04-07 11:10 PM

ATS - do I have to unplug the unloaded power cord to do a FW up grade

When I start a firmware upgrade it is warning me that I must disconnect the unloaded power cord on a AP7750A ATS or it may cause failure or damage the ATS.

(CID:123998813)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:10 PM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:10 PM

Dear Mike,

Please follow the instructions provided in the below K-base document for upgrading your ATS firmware version. 

http://www.schneider-electric.co.in/en/faqs/FA156178/

Regards,

Bala

(CID:123998820)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

Thank you.  ☹️

That's pretty tough to accomplish during business hours and when your 2000 miles away.

(CID:123998835)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

Which versions are you trying to upgrade between and what is the load (amps) on the ATS? Is the power generally stable at the location, maybe fed by a UPS?

We might be able to confirm the risk to you with doing it remotely (unable to remove secondary source) with this information and you can decide if you'd like to still perform the upgrade while understanding the risk.

(CID:123998843)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

Angela, I have about 224 of these in 5 states. I just installed the Struxureware on the 21st. I’ve done my discoveries and added all the equipment. UPS upgrades went fine.

On the ATS’s I have ap7750, and AP7750A versions, the AP7750s took the firmware upgrades with out giving me the warning and I haven’t had any issues.

The AP7750A models are the ones warning me. I realize that the 7750 have a replaceable management card and the 7750A are integrated and that may be the whole difference.

They (both models) are at Application v2.6.1 now. The AP7750A are the only model that showed up when I ran the check today (aprox 94 of them), so I’m not sure I want to take the risk.

All of the ATS are hooked to UPS and Shore power with the UPS power as the proffered source. Amps very between 2 and 4, the bigger branches have more switches.

Power is generally stable.

 

I’m new at this so are there flash versions and application versions?

The update window shows the “Current Version” on the 7750A as 3.71/3.7.4. I’m sure that means current and update to. But when I just look at all ATS in the device window they say they are at Application Version 2.6.1.

 

 

Any help you can give me would be appreciated.

 

 

Thank you,

M7E.

(CID:123998889)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

Hi Mike,

Sure, I can help you. So, AP7750 are older. They do have removable management cards but you can only replace it with the same thing that only supports 2.6.1 application. That is the latest for that model so no upgrade there. They also are a different architecture and design than the successor, AP7750A. Not to make things more confusing but we have AP44XX series ATS replacing AP7750A and other SKUs in its family at the end of this month. So, AP4450 may be a model you get some day soon that replaces AP7750A. That also has a different firmware on our Network Management Card 2 (NMC2) platform and this requirement to remove the secondary source is not required.

 

Anyway for what you have - each ATS - AP7750 or AP7750A has two main firmware versions on it - an AOS (APC Operating System) and an App (Application).  This also applies to any of our other products that use the APC Network Management Card (NMC) technology. They all have an AOS and then the application module name/file changes depending on your device - ATS, UPS, Rack PDU, etc. In StruxureWare, the apply firmware updates window shows you both versions. In device view, you'll only see application version I think.

I have an AP7750A and the latest version is AOS 3.9.2/app 3.9.2. This risk is low with these remote upgrades depending on your upgrade path because not all upgrades include an ATS controller update. I was asking about this so I know your upgrade path. If the ATS controller is not upgraded, it would just be an NMC upgrade itself which can be done with low risk. If there is an ATS controller upgrade completed, the concern is that when you're applying the upgrade, the ATS can start switching back and forth and ultimately botch the firmware upgrade and brick it.

We have the procedure published that Bala sent just to provide the safest way for everyone to do the upgrade with the least amount of criteria to meet. That is why if we can look at your case, we can at least make an educated choice to move forward (or not).

The more recent ATS upgrades have only been NMC for the most part. The easiest thing will be if you can double click on one of your ATS units to log in and go to Unit->About ATS and see what the controller version is. Mine is 3.0.7 and it has all the latest so if yours is not 3.0.7, then we should not proceed as a controller upgrade will occur and you should truly follow the procedure we shared. I have a feeling though one of the two upgrades you need does include a controller update because I can only find 3.0.5 mentioned in these other upgrades. See my ATS here for reference on what I suggest we check on yours:

If the load is lower on these ATSs, the risk is also slim to run into problems but I would still recommend doing the recommended procedure.

Let me know if you have any other questions.

P.S. here are the release notes for the latest version http://www.apc.com/salestools/JKUR-78YSZ3/JKUR-78YSZ3_R4_EN.pdf  and then the one before that http://www.apc.com/salestools/archived/JKUR-78YSZ3/JKUR-78YSZ3_R3_EN.pdf (you're two revisions old since you said you have 3.7.1./3.7.4 which is 'g2ats' app 3.7.1/AOS 3.7.4.

(CID:123998942)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

Thank you, you were spot on. Checked 10 and all were 3.0.5.

 

M7E.

(CID:123998955)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

Hi Mike - OK, so to confirm, we should probably not proceed without unplugging the secondary source as to not damage the ATS when it upgrades to ATS controller 3.0.7. ☹️ 

(CID:123998957)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2024-04-07 11:09 PM

Agreed, I'll probably leave them as they are until I have any issues.

M7E.

 

(CID:123998959)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2023-10-20 04:58 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:13 PM . Last Modified: ‎2023-10-20 04:58 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore