Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

3 Phase to Single Phase Modelling

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure IT
  • EcoStruxure IT forum
  • 3 Phase to Single Phase Modelling
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Jef
Captain Jef Captain
76
APC_Steve
Commander APC_Steve Commander
54
gsterling
Commander gsterling Commander
49
Cory_McDonald
Lt. Commander Cory_McDonald Lt. Commander
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:44 PM

0 Likes
6
533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 11:44 PM

3 Phase to Single Phase Modelling

This question was originally posted on DCIM Support by Stuart Welsby on 2019-11-22


Hi,

 

Does someone know how the best way to model a single phase rack pdu such as an AP8853 from an individual breaker on a 3 phase room pdu?

This environment is in the UK, so the room PDU takes a 415V Three Input and can then output on single phase breakers at 240V for instance.  

 

Edit - To clarify the issue is more around that we are always getting an error as below and would like to clear these.

'The rack pdu output voltage setting does not match the output voltage on the connected PDU '

 

Thanks

Stuart

(CID:152077818)

Labels
  • Labels:
  • Data Center Operation
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:44 PM

0 Likes
4
533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 11:44 PM

This answer was originally posted on DCIM Support by Jef Faridi on 2019-11-22


Hi Stuart,

In the following example I have a simple modeled/configuration: UPS > PDU > r-PDU , where I want to connect my PDU breaker position 2 to rack pdu (AP8853)

1- In PDU properties > Power > Breaker Panel, defined/added Panel (1)

2- select the appropriate configuration under Breaker (2)

3- Under the "Power Consumer" & the appropriate breaker position, click and select the consumer (rack pdu)  (3)

We can verify that the rack-pdu is now connected:

Similar power connection/configuration can also be done from rack-pdu side. 

Kind regards

(CID:152077855)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:44 PM

In response to DCIM_Support
0 Likes
0
533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 11:44 PM

This comment was originally posted on DCIM Support by Stuart Welsby on 2019-11-22


Hi Jef,

 

Thanks for the swift reply.  Apologies though as I didn't describe the problem that well.  We have done the mapping as per your example.  The issue we are wanting to move past is the below error on every cabinet/rPDU connected to the PDU.

"The rack pdu output voltage setting does not match the output voltage on the connected PDU"

As the PDU is three phase it isn't giving us an option to select a single phase output voltage of 240V.

 

Have you come across this before ?

(CID:152078254)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:44 PM

In response to DCIM_Support
0 Likes
0
533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 11:44 PM

This comment was originally posted on DCIM Support by Greg Sterling on 2019-11-22


Hello Stuart.

Did you also edit the output voltages on the rack pdu's to match? 

The default may look like this

I removed the 208 single entry and replaced it with entries for 230 like this. This seems to resolve the warning for me.

Regards

Greg Sterling

(CID:152078256)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:44 PM

In response to DCIM_Support
0 Likes
0
533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 11:44 PM

This comment was originally posted on DCIM Support by Stuart Welsby on 2019-11-29


Hi Greg,

Thank you for responding and apologies for my slow reply.

 

I checked that one out and it was at 230V,  I am thinking it is because its a single phase rPDU and the actual area PDU is a 3 phase board where the output voltages are all marked down , even though you can put single phase generic breakers in it.

All our AP7175 in lines are not reporting the error....

Room PDU Output Voltages

 

 

Thanks

Stu

(CID:152080146)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:44 PM

In response to DCIM_Support
0 Likes
0
533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 11:44 PM

This comment was originally posted on DCIM Support by Jef Faridi on 2019-12-02


Hi Stu,
If I understand correctly your rack pdu output voltage might be 240 V (and not 230 (115)), however if you add 230 and 240 V (single phase) to your rack pdus output voltages:

so they are included in rack pdu Voltage Outputs:

then I guess that may resolve the issue. 

Otherwise it would be great to know little about your setup, so I can test it, then the following screen captures could be useful:

PDU:

PDU, properties > Power
PDU, properties > Power > Breaker Panel


and the problem rack pdu:

rack pdu, properties > Power
rack pdu, properties > Power Dependencies

Kind regards

(CID:152080587)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:44 PM

0 Likes
0
533
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-05 11:44 PM

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Share
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc