Hello,
How do I do a factory reset on a netbotz250?
I don't see any field under the network tab with that option, and the help manual does't help also.
Thanks.
Ricardo
(CID:136644577)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:25 PM . Last Modified: 2024-04-03 11:55 PM
Dear Ricardo,
Are you looking for this option?

(CID:136644585)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:25 PM . Last Modified: 2024-04-03 11:55 PM
Hello Balaraman,
Thanks for the answer, I was looking at that, but it doesn't work, I suspect I have a hardware failure.
Thanks for the answer
Ricardo.
(CID:137108871)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:25 PM . Last Modified: 2024-04-03 11:55 PM
Hi Ricardo,
Good day!
If the steps described by Bala did not seem to help. You can issue a telnet/SSH command on the NMC to reset it to defaults.
apc>resettodef ? Usage: resetToDef -- Configuration Options resetToDef -p
If this still does not help, deleting the database manually and/or issuing a format command can also be done via telnet or SSH to wipe the flash memory and any remaining configurations including your current TCP/IP settings.
The instructions are explained in detail from the article from the link below:
https://www.schneider-electric.us/en/faqs/FA175980/
I hope this helps.
Kind regards,
Justine Chester
(CID:136644876)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:25 PM . Last Modified: 2024-04-03 11:55 PM
Hi Ricardo, In addition to Justin's answer, I suggest to make sure that you are using the administrator user name and password when you are doing the steps. It is most likely not related to hardware issue.
(CID:137108873)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:25 PM . Last Modified: 2023-10-22 09:32 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.