Why doesn't DCE keep a catalog of firmware updates?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Why doesn't DCE keep a catalog of firmware updates?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
5
1140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

Why doesn't DCE keep a catalog of firmware updates?

I suppose this is a feature request, but we routinely can't access the update site from DCE which makes pushing firmware a convoluted process at times. 

This would be simpler if DCE would keep a backup copy of the catalog for when it can't reach the update site. 

(CID:110018392)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

Hi Sam,

 

StruxureWare will go out and find the most recent firmware when you request it...assuming it can reach the site. If it does reach the site, it will download what is available. Those downloads are not deleted. If you download a 6.4.x version of firmware and do not use it, the system does not delete it, it remains in the system. 

 

If the system can not reach the site but you need the most recent updates available, you can also go to www.apc.com/tools/download and download a zip file version of the catalog. Please keep in mind that both the DCE hitting the update server as well as the catalog file do not always have the most recent versions of the available device firmware. DCE's update and the catalog update can only be configured after the individual files are made available for download and at times it may be a few weeks until the latest is available in either form of the catalog.

 

Thanks,

Steve.

(CID:110018406)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

Hi Sam,

 

StruxureWare will go out and find the most recent firmware when you request it...assuming it can reach the site. If it does reach the site, it will download what is available. Those downloads are not deleted. If you download a 6.4.x version of firmware and do not use it, the system does not delete it, it remains in the system. 

 

If the system can not reach the site but you need the most recent updates available, you can also go to www.apc.com/tools/download and download a zip file version of the catalog. Please keep in mind that both the DCE hitting the update server as well as the catalog file do not always have the most recent versions of the available device firmware. DCE's update and the catalog update can only be configured after the individual files are made available for download and at times it may be a few weeks until the latest is available in either form of the catalog.

 

Thanks,

Steve.

(CID:110018406)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

I second Sam's question. I use the offline file where I download the file and then I have to upload it into DCE. It seems random when I go into DCE to push a firmware and the files are gone.

I then have to upload the file again. I haven't found a rhyme or reason why. Seems like a bug to me.

The issue I have is multiple people push firmware files however I am the only one who knows where the zip file is located to upload it into the server. That is so I can ensure the latest file it uploaded. So I am constantly getting calls to re-upload the file because DCE drops it for some reason.

 

Regards,

J

(CID:110019122)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:09 AM . Last Modified: ‎2025-05-27 11:04 PM

0 Likes
0
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:09 AM . Last Modified: ‎2025-05-27 11:04 PM

Hi John,

 

I have not seen where the files just disappear. I do know that if the devices are upgraded, they won't show that they are able to be upgraded again. If a device runs 6.2.x firmware and the catalog has 6.4.x, it should show that the device has the available upgrade. After the upgrade, that device should no longer show upgrade options. f you add a new device with older firmware however, it should indeed show the upgrade as an option.

 

I do recall seeing starting in 7.2 that if you upload the catalog and then choose the option to check for updates and you do not have update capabilities (can not connect to updates.apc.com with DCE) that the update would disappear and they're looking into that. It is noted in k-base FA239230.  If you know there is no connectivity, please make sure they don't keep trying the update option 

 

Steve

(CID:110019126)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:09 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:09 AM . Last Modified: ‎2024-04-08 02:39 AM

P.S.

If you do have issues connecting, make sure there is no scheduled checks for updates (noted in k-base too)

 

Steve

(CID:110019128)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:09 AM . Last Modified: ‎2023-10-22 04:21 AM

0 Likes
0
1141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:09 AM . Last Modified: ‎2023-10-22 04:21 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore