ETL export not working in 8.0.2

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • ETL export not working in 8.0.2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:06 AM . Last Modified: ‎2024-04-08 02:40 AM

0 Likes
13
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:06 AM . Last Modified: ‎2024-04-08 02:40 AM

ETL export not working in 8.0.2

After upgrading to 8.0.2 my ETL export database is no longer functioning. I think it's a driver issue at this point, but I can't get the MS JDBC driver to upload via webmin. This was working without issue until the upgrade.

 

The instructions here: https://dcimsupport.apc.com/display/public/DCIMDEVELOPER/ETL+export+to+MS+SQL+Server aren't very helpful. The driver they point to hasn't been updated since 2013.

 

The MS SQL drivers can be found here: https://msdn.microsoft.com/en-us/library/mt484311(v=sql.110).aspx , but again, I can't get it uploaded.

(CID:110018386)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
1
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

Hi Sam

So the issue with uploading the driver is actually fixed in 8.0.3. However when we tested that driver it did not work as the driver does not support save points.

My recommendation is that you use the jtds driver pointed to in the link in your original post. Or is there a reason why you cannot use that?

Due to the upgrade issue you have encountered (did you upgrade from 7.5 or 8.0?), I recommend that you delete the current ETL export system and database and setup a new one.

Best,
Niels

(CID:110020757)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:40 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:40 AM

Hi Sam

The ETL DBs are not to be considered permanent.  In my experience, the DBs are often simply stopped after a DCO upgrade.  I hit the start button for each DB in webmin and things are usually OK.  Then I check via command line the DB is functioning and the data is present, then I check remote connections, usually first via a remote GUI access tool like pgadmin.

 I would expect a driver or some other change affecting remote access to have been documented in the release notes.

Cheers

Ed

(CID:110018455)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

Hi Ed, thanks for your response.

I did the restart immediately after the upgrade and everything looked fine. It said it started, all showed green. (This is still the initial behavior when I try to start the DB)

It was only when I started making updates in the system that I noticed the external system wasn't staying in sync with DCO.

My primary reason for thinking it's a driver issue is that the JDBC driver doesn't show up as an option when I go to add a new external connection, only the native postgres driver is listed. Since 8.0.2 was a new OS install from 7.x it probably wouldn't carry over with a backup/restore.

(CID:110018461)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

Hmmmm, strange

Perhaps lets ascertain if it's a problem with DCO to Export DB or Export DB to remote client

Make and save a small change to DCO.  Then perform a manual update of the ETL export DB.  Then check if the data is present using command line.  Let me know if you need help here

 

(CID:110018466)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

I'll need help getting to the data - I'm not very strong on Linux or postgres. I do think it's an issue with the DCO exporting.  I can connect to the remote DB from another system and login with the configured user account and make updates.

(CID:110018475)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

Sam, the image shows the DB in "Error".    This will need to be addressed before proceeding

Perhaps delete the DCO external system, destroy the DB then recreate the both and populate.  You may need to re-establish remote comms

Else you may need to get factory support to diagnose the issue.

(CID:110018481)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

Hi Ed,

I called support and they asked me to post in the forums because the external DB isn't part of the standard config. Unfortunately I can't recreate the DB because it isn't letting me add the JDBC driver.

 

The DB doesn't error out immediately - it seems to work fine until the scheduled update (hourly).

(CID:110018494)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

Can anyone else assist? 

(CID:110018523)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:07 AM . Last Modified: ‎2024-04-08 02:39 AM

Hi Sam

Can you say exactly which steps you have taken when trying to add the driver? For example there was one issue where the driver was not unpacked before being uploaded to the DCO server.

Best,

Niels

(CID:110018784)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

Hi Niels,

I downloaded the driver package from MS, unzipped it, found the right version, unzipped it again(they had run a tar through gz), and uploaded it through the webmin. The webmin never acknowledged the upload succeeded. 

(CID:110018908)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

More details on the upload issues:

When I attempt to upload a .jar file the browser hangs (happens in chrome and ie)

I can upload a .tar file, but after rebooting the driver isn't listed as available and nothing shows up in the directory from the support page. 

 

Is there a way to upload the .jar driver file using the normal webmin upload/download module instead of the ETL driver add page?

(CID:110019914)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

0 Likes
1
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

Hi Sam

So the issue with uploading the driver is actually fixed in 8.0.3. However when we tested that driver it did not work as the driver does not support save points.

My recommendation is that you use the jtds driver pointed to in the link in your original post. Or is there a reason why you cannot use that?

Due to the upgrade issue you have encountered (did you upgrade from 7.5 or 8.0?), I recommend that you delete the current ETL export system and database and setup a new one.

Best,
Niels

(CID:110020757)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

In response to DCIM_Support
0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2024-04-08 02:39 AM

Hi Niels,

Thanks for your answer - that seems to have corrected the issue completely. Surprisingly I did not need to recreate the external db setup, it just started working once I got the driver uploaded.

(CID:110790408)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2023-10-22 01:57 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:08 AM . Last Modified: ‎2023-10-22 01:57 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore