Where to find tftpraptor2.6.2.zip for a netbotz 500 ?
(CID:103585390)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:28 PM . Last Modified: 2024-04-09 02:48 AM
Hello Simon,
Here is location and instructions to reflash the NetBotz 500.
Download this file: http://www.netbotz.com/updates/patches/bw/2.6.2/tftpRaptor262.zip
This must be run from a computer on the same network segment as the Netbotz device.
1.) Extract the file you have downloaded to a temp folder on your pc.
2.) Next run the tftpd32.exe. Tftpd32.exe sets up a temporary tftp server on your PC. It will also show you what your computer’s IP is. This will be necessary for steps below. Make sure there are no firewalls blocking tftp ports.
3.)You should do the upgrade via the post-mechanism using Windows Hyperterminal with these settings: Bits/Sec=38,400, 8, N, 1, Hardware. Once you get your hyperterminal connected, reboot (power-cycle) your bot and stop the boot at the point where it`s doing the autoboot countdown, 5, 4, 3, 2, 1... (it will tell you to hit enter and just do so before the countdown expires).
4.)At this point (NetBotz> prompt should appear) you will type the following in to tell the appliance where to get the code from:
setenv serverip (ip_of_pc_running_tftpd32.exe)
5. NOTE: Items with a "" prefix mean you only need to use these commands if the network you're plugged into doesn't support DHCP or because of a firmware issue, the Bot cannot obtain a DHCP address. If you do have DHCP, the appliance should obtain an IP address.
*setenv ipaddr (IP of the address you want to assign the bot)
*setenv gatewayip (IP of gateway)
*setenv netmask (Subnet Mask IP)
saveenv (this will save the environmental variables you have just changed)
printenv (this will print out your settings for verification
6.Now initiate the first part of the upgrade.
postupg (wait for the NETBOTZ> prompt before continuing)
7. At this point initiate the 2nd part of the upgrade procedure:
kernupg (wait for the NETBOTZ> prompt before continuing)
8. Now the last part of the upgrade procedure can be initiated.
rootupg (this final upgrade option will wipe out all Bot configuration)
After the rootupg finishes installing, your system will automatically reboot and you should be able to assign/configure an IP address to the appliance and now fully configure the device as needed.
Thanks
Victor
(CID:103585392)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:28 PM . Last Modified: 2024-04-09 02:48 AM
Hello Simon,
Here is location and instructions to reflash the NetBotz 500.
Download this file: http://www.netbotz.com/updates/patches/bw/2.6.2/tftpRaptor262.zip
This must be run from a computer on the same network segment as the Netbotz device.
1.) Extract the file you have downloaded to a temp folder on your pc.
2.) Next run the tftpd32.exe. Tftpd32.exe sets up a temporary tftp server on your PC. It will also show you what your computer’s IP is. This will be necessary for steps below. Make sure there are no firewalls blocking tftp ports.
3.)You should do the upgrade via the post-mechanism using Windows Hyperterminal with these settings: Bits/Sec=38,400, 8, N, 1, Hardware. Once you get your hyperterminal connected, reboot (power-cycle) your bot and stop the boot at the point where it`s doing the autoboot countdown, 5, 4, 3, 2, 1... (it will tell you to hit enter and just do so before the countdown expires).
4.)At this point (NetBotz> prompt should appear) you will type the following in to tell the appliance where to get the code from:
setenv serverip (ip_of_pc_running_tftpd32.exe)
5. NOTE: Items with a "" prefix mean you only need to use these commands if the network you're plugged into doesn't support DHCP or because of a firmware issue, the Bot cannot obtain a DHCP address. If you do have DHCP, the appliance should obtain an IP address.
*setenv ipaddr (IP of the address you want to assign the bot)
*setenv gatewayip (IP of gateway)
*setenv netmask (Subnet Mask IP)
saveenv (this will save the environmental variables you have just changed)
printenv (this will print out your settings for verification
6.Now initiate the first part of the upgrade.
postupg (wait for the NETBOTZ> prompt before continuing)
7. At this point initiate the 2nd part of the upgrade procedure:
kernupg (wait for the NETBOTZ> prompt before continuing)
8. Now the last part of the upgrade procedure can be initiated.
rootupg (this final upgrade option will wipe out all Bot configuration)
After the rootupg finishes installing, your system will automatically reboot and you should be able to assign/configure an IP address to the appliance and now fully configure the device as needed.
Thanks
Victor
(CID:103585392)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:28 PM . Last Modified: 2024-04-09 02:48 AM
Hello Simon, I just noticed that the download location is no longer up. Here is a new location, https://schneider-electric.box.com/s/ypqmnq6ytgwgoc52c5jy Thank Victor
(CID:103585393)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:28 PM . Last Modified: 2024-04-09 02:48 AM
Thanks for your help but download link is not working. It's why i'm asking...
(CID:103585422)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:28 PM . Last Modified: 2024-04-09 02:47 AM
Thank you !!
(CID:103585397)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:28 PM . Last Modified: 2024-04-09 02:47 AM
I'm also looking for tftpRaptor262.zip. Please advise where this file currently resides.
(CID:110005821)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:28 PM . Last Modified: 2024-04-09 02:47 AM
The link is dead ??
http://www.netbotz.com/updates/patches/bw/2.6.2/tftpRaptor262.zip
Need this file !!
(CID:116362794)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:28 PM . Last Modified: 2024-04-09 02:47 AM
I need this one to 😀
http://updates.netbotz.com/patches/bw/2.6.2/tftpCobra262.zip
Seems that the link there is dead ??
(CID:116362799)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:29 PM . Last Modified: 2023-10-31 11:44 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.