Posted: 2020-07-03 08:41 AM . Last Modified: 2024-04-08 03:47 AM
Hi there,
I purchased A9335T temperature sensor but not really suite for my requirement. I want to terminate a Schneider STR100 room temp sensor into universal port on Netbotz 570. However I require the correct pinouts to terminate RJ45 into Netbotz. Does anyone have the info on which pinouts/ cable colour to use for termination on temperature sensor?
(CID:110006836)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:41 AM . Last Modified: 2024-04-08 03:47 AM
Hi,
The NetBotz 570 Installation and quick configuration manual can be found
http://www.apc.com/salestools/LSCZ-7BUKZ9/LSCZ-7BUKZ9_R6_EN.pdf
Referring to page 1 you will find the recommended additional options.
You will find the sensors compatible with the NetBotz 570 are
• Temperature Sensor (AP9335T)
• Temperature/Humidity Sensor (AP9335TH)
• Temperature Sensor with Digital Display (AP9520T)
• Temperature/Humidity Sensor with Digital Display (AP9520TH)
(CID:110007552)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:41 AM . Last Modified: 2024-04-08 03:47 AM
Hi Gary,
The STR100 is not compatible with the NBRK0570 and the firmware in the 570 knows nothing about the sensor or how to read it. The "universal" sensor ports are for any sensor listed in the manual as supported that do not have a specific port (like the leak rope). I don't see where this can be monitored by NetBotz but if it has a 4-20 mA output or 0-5v output, NetBotz can read those parameters.
Thanks,
Steve
(CID:110006845)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:41 AM . Last Modified: 2024-04-08 03:47 AM
Gary, the AP9335T Temperature probe will connect directly into the universal RJ45 port on the Netbotz. Note that this will be required to be patched directly into the RJ45, not via a network switch.
The Schneider STR100 is not a componet of the Netbotz range, and will need to use the 4-20 mA output or 0-5v output as Steve indicated. Also as an alternative, the NB range also support wireless Temperature and Temperature/Humidity sensors.
(CID:110006896)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:41 AM . Last Modified: 2024-04-08 03:47 AM
Hi,
The NetBotz 570 Installation and quick configuration manual can be found
http://www.apc.com/salestools/LSCZ-7BUKZ9/LSCZ-7BUKZ9_R6_EN.pdf
Referring to page 1 you will find the recommended additional options.
You will find the sensors compatible with the NetBotz 570 are
• Temperature Sensor (AP9335T)
• Temperature/Humidity Sensor (AP9335TH)
• Temperature Sensor with Digital Display (AP9520T)
• Temperature/Humidity Sensor with Digital Display (AP9520TH)
(CID:110007552)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 08:41 AM . Last Modified: 2023-10-22 04:10 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.