Temperature sensor with display connectivity

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Temperature sensor with display connectivity
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:41 PM . Last Modified: ‎2024-04-09 11:45 PM

0 Likes
3
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:41 PM . Last Modified: ‎2024-04-09 11:45 PM

Temperature sensor with display connectivity

Hi All!

I have an issue with AP9520TH sensors connected to Netbotz 200.

There are three sensors and sensor pod 150 on A-Link bus, each configured with it's own address and at sensor page I can see only one of them. If I swap sensors, I can see another one, but only nearest to appliance in the chain and have message about previous sensor disconnecting.

 

Sensors are "new" type, with 2.1.4 firmware.

I assume that it is a cabling problem and try to replace all cables tomorrow, but maybe there is another reason?

Did you have similar issue?

(CID:96764507)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:41 PM . Last Modified: ‎2024-04-09 11:45 PM

0 Likes
0
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:41 PM . Last Modified: ‎2024-04-09 11:45 PM

Hi Valentin,

 

I have seen where customer may hold the unit up-side-down when configuring the dip switches. Please be sure when looking at them and when matching them up with the manual, make sure the APC sticker is facing up. Make sure they're numbered differently. Other than that, please make sure you are using CAT-5/CAT-5E cables. If you are using CAT-6, you're likely to have comm issues. If you also have sensor pod 150s connected, try removing them for testing purposes. If you have too many things on the A-link buss, you may need to power 1 of the 150s  (if exist). You may also want to terminate the string. The 200 should have come with a terminator, I suggest tryong both with and without the terminator in the last sensor.

 

Steve

 

 

(CID:96764513)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:41 PM . Last Modified: ‎2024-04-09 11:45 PM

0 Likes
0
994
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:41 PM . Last Modified: ‎2024-04-09 11:45 PM

Hi Valentin,

 

I have seen where customer may hold the unit up-side-down when configuring the dip switches. Please be sure when looking at them and when matching them up with the manual, make sure the APC sticker is facing up. Make sure they're numbered differently. Other than that, please make sure you are using CAT-5/CAT-5E cables. If you are using CAT-6, you're likely to have comm issues. If you also have sensor pod 150s connected, try removing them for testing purposes. If you have too many things on the A-link buss, you may need to power 1 of the 150s  (if exist). You may also want to terminate the string. The 200 should have come with a terminator, I suggest tryong both with and without the terminator in the last sensor.

 

Steve

 

 

(CID:96764513)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:41 PM . Last Modified: ‎2024-04-09 11:45 PM

0 Likes
0
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:41 PM . Last Modified: ‎2024-04-09 11:45 PM

It was a cabling issue. After replacing cables with new ones CAT-5, system works as expected.

(CID:96764564)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:41 PM . Last Modified: ‎2023-10-31 11:38 PM

0 Likes
0
993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:41 PM . Last Modified: ‎2023-10-31 11:38 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore