Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Synology SNMP v3 Monitoring in EcoStruxture Gateway

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Synology SNMP v3 Monitoring in EcoStruxture Gateway
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:26 AM . Last Modified: ‎2024-04-02 11:34 PM

0 Likes
5
2186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:26 AM . Last Modified: ‎2024-04-02 11:34 PM

Synology SNMP v3 Monitoring in EcoStruxture Gateway

Synology is one of the largest NAS manufacturers Top 3 brands and including china top 10 manufacturers.

We run all sites with APC SMT1500IC UPS backup and need to see if the server are alive - the UPSes are fine for cloud and SNMP v3 protocols:

BUT the Snyology brand is not supported in EcoStruxture Gateway.

That is a major issue for us and we dont have an easy way to monitor both natively in the same software - is there a way to implement the SNMP ping in EcoStruxture as its not supported?

Can I import the MIB files?

 

 

(CID:153093232)

Labels
  • Labels:
  • IT Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:26 AM . Last Modified: ‎2024-04-02 11:34 PM

0 Likes
0
2187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:26 AM . Last Modified: ‎2024-04-02 11:34 PM

Dear David Radszuweit,

As you rightly noted, there is no simple native solution now (I suppose that in the near future, it will not be either).

The fact is that EcoStruxure IT Gateway software and corresponding =SE= EcoStruxure IT Expert cloud service is designed to monitor the engineering infrastructure of data centers (UPS, conditioners, rPDU, environment, and much more), but not IT equipment (servers, storage, switches, etc.).

It is possible that EcoStruxure IT Gateway software will open up the possibility of monitoring IT equipment inherent in it, but when it will not be known... But the ability to import custom MIB or DDF files into this software was initially disabled. Therefore, it is impossible to do this.

Therefore, you need to look for some workarounds so that you can monitor the availability of your NAS, for example through NMC in the Smart Slots of your UPS. This may be an option for reflection.

You can also tell =SE= about your wishes on the special web resource ECOSTRUXURE IT SUPPORT > ECOSTRUXURE IT GATEWAY by clicking Submit a ticket.

If you have more questions, please ask.

With respect.

(CID:153093244)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:26 AM . Last Modified: ‎2024-04-02 11:34 PM

0 Likes
0
2188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:26 AM . Last Modified: ‎2024-04-02 11:34 PM

Dear David Radszuweit,

As you rightly noted, there is no simple native solution now (I suppose that in the near future, it will not be either).

The fact is that EcoStruxure IT Gateway software and corresponding =SE= EcoStruxure IT Expert cloud service is designed to monitor the engineering infrastructure of data centers (UPS, conditioners, rPDU, environment, and much more), but not IT equipment (servers, storage, switches, etc.).

It is possible that EcoStruxure IT Gateway software will open up the possibility of monitoring IT equipment inherent in it, but when it will not be known... But the ability to import custom MIB or DDF files into this software was initially disabled. Therefore, it is impossible to do this.

Therefore, you need to look for some workarounds so that you can monitor the availability of your NAS, for example through NMC in the Smart Slots of your UPS. This may be an option for reflection.

You can also tell =SE= about your wishes on the special web resource ECOSTRUXURE IT SUPPORT > ECOSTRUXURE IT GATEWAY by clicking Submit a ticket.

If you have more questions, please ask.

With respect.

(CID:153093244)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:26 AM . Last Modified: ‎2024-04-02 11:34 PM

0 Likes
2
2187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:26 AM . Last Modified: ‎2024-04-02 11:34 PM

Submitted.

I really just need to ping the SNMP v3 protocol.

Irritating as it says it finds and logs in to the device but do not support it.

(CID:153093249)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:26 AM . Last Modified: ‎2024-04-02 11:34 PM

In response to DCIM_Support
0 Likes
0
2187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:26 AM . Last Modified: ‎2024-04-02 11:34 PM

Dear David Radszuweit,

So, this is correct, i.e. EcoStruxure IT Gateway does not have a corresponding DDF-file for this device. And there are no more restrictions.

Let's hope that the developers of this software will hear the wishes of the DCIM community.

With respect.

(CID:153093261)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:27 AM . Last Modified: ‎2024-04-02 11:34 PM

In response to DCIM_Support
0 Likes
0
2187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:27 AM . Last Modified: ‎2024-04-02 11:34 PM

Hi David,

You can request a DDF creation to support Synology products to our Engineering team.

There are 2 paths for DDF creation today:

  1. Free delivery (no estimation for delivery date, it can vary from 3 to 6 months, devices are selected based on amounts of requests for it)
  2. Paid delivery (DDF is expedited) - Agreed upon delivery to deliver faster and prioritize device model (Please reach out to your local CSM to help you with this request)

How to submit a free DDF creation:

***To support a Modbus device in ITE:

We need you to attempt running a discovery in the Gateway, then enable targeted reads for support (instructions here).  We also need the Register Maps.

Please go to: https://ddf.ecostruxureit.com/create

Fill out the information and submit the request.

 

***To support an SNMP device in ITE:

We need you to attempt running a discovery in the Gateway so we can get the walk, or please generate the walk file manually (instructions on here).

Please go to: https://ddf.ecostruxureit.com/create

Fill out the information and submit the request.

 

Best regards

Charlotte Arroyo

(CID:153550901)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-06 12:27 AM . Last Modified: ‎2023-10-22 04:05 AM

0 Likes
0
2187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 12:27 AM . Last Modified: ‎2023-10-22 04:05 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore