StruxureWare does not discover Netbotz 570

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • StruxureWare does not discover Netbotz 570
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:14 AM

0 Likes
8
1239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:14 AM

StruxureWare does not discover Netbotz 570

Hello! 

 

I've recently installed a StruxureWare VM and a Netbotz 570 in our datacenter. For some reason StruxureWare will not discover the 570, which is on the same subnet as the StruxureWare VM. I have other Netbotz devices at remote locations that are discovered with no problem. Any idea why the 570 would not show up? 

I can access the 570 with the NetBotz Advanced View software, so I assume it is functioning correctly. 

(CID:122094230)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

0 Likes
4
1240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

Hi Sam,

 

There is no reason for DCE to be unable to discover a NetBotz 570. Things you need  to verify first however are things like:

  • Are there enough node licenses available on DCE?
  • Are you providing the correct admin user name and password during discovery?
  • Are you using the correct protocol (ie HTTP / HTTPS VS SNMP)?
  • Does your VM or router have specific firewall rules that could be blocking communications between the 2 systems?
  • What version DCE? What version Botzware on the 570?

If this same server can discover devices in a remote network but not on it's own segment, it is likely something in the configuration as suggested in the above questions.

 

Thanks,

Steve

 

 

(CID:122094239)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

In response to DCIM_Support
0 Likes
0
1239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

Hi Steve, thanks for the reply! 

  • We are good on licenses.
  • Credentials are correct. As mentioned, I can log in from the Netbotz Advanced View software. 
  • When creating the discovery, I used the "Netbotz Appliance" option. Should I use something else? 
  • The VM does not have a firewall between it and the 570 appliance unless there is a firewall built into the VM that I'm not aware of. 
  • DCE is version 7.4.3, Netbotz 570 is 4.5.4.

Agreed that it's most likely a configuration issue, I'm just not sure where. Any other ideas? 

(CID:122094698)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

In response to DCIM_Support
0 Likes
0
1239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

Hi Sam,

No, that's the correct discovery type. Some times people try adding a 570 using an SNMP discovery, I just wanted to verify you're not doing that. The 200 and 250 would use SNMP though (I know, may be confusing) but not the 3xx, 4xx, and 5xx series units.

You may also want to double-check the IP Filter applet on the NetBotz appliance. That's a firewall too.

If you've backed up the NetBotz appliance, you can also try resetting the config just to be sure there's nothing corrupt or wrong with the bot. To do this without changing the IP of the appliance (It will wipe out everything else...that's why you back it up) just go to the web page of the appliance and append /unconfig or http:///unconfig as per k-base FA158175.

The other thing you can try is to use the "Post-Only mode" option. This is on the NetBotz appliance under Tools -> Advanced.

What post only mode does is it causes the NetBotz to initiate communications instead of the DCE server. Much like when you're on the internet, an internet site can't start communications with your computer until your computer initiates that contact. If this works, then there's likely something blocking the DCE server from reaching out to the bot using HTTP or HTTPS. 

 

Steve

(CID:122094715)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

In response to DCIM_Support
0 Likes
0
1239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

Hey Steve, 

 

Sad to report that I've tried all options above and have still had no luck. Is it possible there is a problem with the 570? Do I need to open a ticket with support. 


The only other issue I can think of is that I haven't been able to register the 570 since it does not have a connection to the internet. Would that make any difference? 

(CID:122095220)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

In response to DCIM_Support
0 Likes
0
1239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

Hi Sam,

DCE communicates with the NetBotz using the same protocol used by advanced view and by the web. If you can access the appliance using those options, there is no reason on the appliance that it should not communicate with DCE. A hardware issue wouldn't cause this and still allow web and Advanced View.

 

I doubt it's a firmware issue but you may also want to try to re-flash the firmware and wipe out all data and potential corruption. K-base FA176133 can walk you through that procedure. Do not use the "keep" option and do not re-import any backups.

 

Registration of the appliance does not matter when it comes to communications, only for potential support and license key activation purposes. 

 

You can always open a ticket with your local support and they'll work through this type of troubleshooting with you. Maybe being on the phone at the time of troubleshooting will help. It's also possible that a remote session can be established and they can actually see and better understand what it happening. 

 

Steve

(CID:122095227)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

0 Likes
0
1240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

Hi sam.killian,

Have you solved the problem or not? And if so, how?

With respect.

(CID:122096008)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

0 Likes
0
1240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:23 PM . Last Modified: ‎2024-04-08 12:13 AM

I have not. I will contact support and report back but I've had other, more pressing issues come up, so I have not had a chance to speak to anyone. 

(CID:122096266)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:24 PM . Last Modified: ‎2023-10-22 04:02 AM

0 Likes
0
1240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:24 PM . Last Modified: ‎2023-10-22 04:02 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore