Still having 6.4.6 SNMPv3 issues... when is 6.5.0 coming out?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Still having 6.4.6 SNMPv3 issues... when is 6.5.0 coming out?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:58 PM . Last Modified: ‎2024-04-08 12:01 AM

0 Likes
7
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:58 PM . Last Modified: ‎2024-04-08 12:01 AM

Still having 6.4.6 SNMPv3 issues... when is 6.5.0 coming out?

I'm still suffering about 2000 devices worth of "Lost Communication" in DCE 7.4.3 due to SNMPv3 bugs in 6.4.6 and rebooting the server constantly is getting troublesome.

Please see https://www.apc.com/us/en/faqs/FA305661/

According to this FAQ, 6.5.0 won't have this issue. Can anyone give me an ETA? I'm about ready to start downgrading all my devices. What version FW doesn't have this issue?

 

Also, has 6.4.6 been removed in general? I noticed that DCE 7.4.3 only offers 6.4.0 in it's firmware update tool.

(CID:122690043)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:58 PM . Last Modified: ‎2024-04-08 12:01 AM

0 Likes
5
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:58 PM . Last Modified: ‎2024-04-08 12:01 AM

Hi Travis,

 

I don't have an exact date but it looks right now as f the firmware release for the NMC should be within the next week or two. As with everything, these dates could change but that's the way it looks today.

 

Thanks,

Steve

(CID:122690425)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2024-04-08 12:01 AM

In response to DCIM_Support
0 Likes
0
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2024-04-08 12:01 AM

...and yes, because of the SNMP issue, it was removed from the firmware catalog.

(CID:122690431)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2024-04-08 12:01 AM

In response to DCIM_Support
0 Likes
0
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2024-04-08 12:01 AM

Do you have any further detail on a potential release date now that we are a week closer?

(CID:122693753)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2024-04-08 12:01 AM

In response to DCIM_Support
0 Likes
0
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2024-04-08 12:01 AM

Hi Travis,

 

I have no word on when a DCE catalog with firmware may be released. I Know the Smart-UPS firmware  is on the FTP site today and the official download link on the product and downloads page should follow soon. I have no specific information on other firmware at this time but they too should be available soon. I'll mention to product management (although I'm sure they're aware) that people are looking for the DCE firmware catalog.

Edit: That was the SUMX link. I didn't check it out prior to posting...turns out they're both up, Here's the SY firmware.

 

Steve

(CID:122693795)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2024-04-08 12:01 AM

In response to DCIM_Support
0 Likes
0
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2024-04-08 12:01 AM

Is that link for Symmetra or Smart-Ups? I'm looking Smart-ups too.

 

-Travis 

(CID:122693799)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2024-04-08 12:01 AM

In response to DCIM_Support
0 Likes
0
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2024-04-08 12:01 AM

My bad...they're now both up on FTP. Still no PDU2 yet

 

(CID:122693802)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2023-10-22 03:58 AM

0 Likes
0
1158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:59 PM . Last Modified: ‎2023-10-22 03:58 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore