Smoke detector support on NB570

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Smoke detector support on NB570
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:00 AM . Last Modified: ‎2024-04-10 01:02 AM

0 Likes
9
1777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:00 AM . Last Modified: ‎2024-04-10 01:02 AM

Smoke detector support on NB570

How many smoke detectors can I install on NETBOTZ 570? Already tested with some third-party smoke detectors?

(CID:93913767)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

0 Likes
6
1777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

Hi Pablo,

 

When it comes to integrating our Netbotz smoke sensors (NBES0307) to the Netbotz 570, the limit is 2 per pod. The main unit and integrated pod will only see two but once another sensor pod is added and externally powered, you can then add 2 more. The limit is based on the sensor pod limit. 

 

We can also monitor 3rd party smoke sensors using dry contacts, 0-5v output or 4-20 mA output. This is how we integrate 3rd party options that are not specifically Netbotz products. I don't have a recommended 3rd party smoke sensor SKU that has been officially tested, but as long as it is simply a dry contact output, it should be fine to use with our Netbotz products. 

Hope this answers your question. 

 

Regards,

Breda

(CID:93913779)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

0 Likes
0
1777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

Hi NBRK0570 can take maximum 2 Smoke detectors.

(CID:93913770)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

0 Likes
6
1778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

Hi Pablo,

 

When it comes to integrating our Netbotz smoke sensors (NBES0307) to the Netbotz 570, the limit is 2 per pod. The main unit and integrated pod will only see two but once another sensor pod is added and externally powered, you can then add 2 more. The limit is based on the sensor pod limit. 

 

We can also monitor 3rd party smoke sensors using dry contacts, 0-5v output or 4-20 mA output. This is how we integrate 3rd party options that are not specifically Netbotz products. I don't have a recommended 3rd party smoke sensor SKU that has been officially tested, but as long as it is simply a dry contact output, it should be fine to use with our Netbotz products. 

Hope this answers your question. 

 

Regards,

Breda

(CID:93913779)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

In response to DCIM_Support
0 Likes
0
1777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

How do I find the POD 150 limit?

(CID:93913841)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

In response to DCIM_Support
0 Likes
0
1777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

Hi! Breda, is it new feature of Netbotz 570? As I know, it's only two smoke sensors can be connected per appliance, regardless of pod's number. At least Netbotz 550 in setup with six 150 pod's detect only two smoke sensors per system. And in doesn't matter where it's connected - to external pod or to Netbotz appliance.

(CID:93913853)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

In response to DCIM_Support
0 Likes
0
1777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

Pablo, with Netbotz 570 you can cascade up to 12 sensor pods and up to 8 temperature and temperature/humidity sensors with display (AP9520T and AP9520TH).

(CID:93913854)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

In response to DCIM_Support
0 Likes
0
1777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

Hi Valentin, This was recently looked into. When the pod is externally powered, you can add more based on sensor pod limits. The sensor pod limit for the 150 is one smoke sensor.

(CID:93913859)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

In response to DCIM_Support
0 Likes
0
1777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

Pablo, Breda, you can recommend smoke sensors from Schneider: For example, when I need to quote 1 per rack, I use to quote: "EDC-20 Optical Smoke Detector with Sen" + "EBC-20 Relay Base" If you need to quote also a PSU, you can quote for example a "ABL8MEM24012 PSU, 24V, 1.2A" that will feed lots of smoke sensors.

(CID:93914013)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

In response to DCIM_Support
0 Likes
0
1777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2024-04-10 01:02 AM

Hi Breda, if I understand properly, in case I need to connect 4 Smoke Sensors NBES0307 to a Netbotz 450, I would need to add 2 Sensors Pods 150 (since 2 Smoke Sensors is the limit for Netbotz 450 while 1 Smoke Sensors is the limit for the Netbotz 150). Is my understanding correct? Thanks a lot

(CID:99156876)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2023-10-31 11:35 PM

0 Likes
0
1777
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:01 AM . Last Modified: ‎2023-10-31 11:35 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore