I would need to connect 4 Smoke Sensors (NBES0307) to a Netbotz 450. Due to the limit of 2 sensors for the Netbotz 450, would it work to add to it 2 Netbotz Sensors Pods 150 (since, if I understand properly, each Netbotz Sensor Pod 150 can support up to 1 Smoke Sensor)?
Thanks a lot
(CID:99157074)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:11 PM . Last Modified: 2024-04-09 04:16 AM
Hi Antonio,
I believe the limit is 2 smoke sensors per pod. If you have just the appliance, your limit is 2. If you have an appliance with 1 sensor pod (and I suggest you use external power), the limit is 4. 2 external pods and the limit is 6 etc.
Steve
(CID:99157076)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:11 PM . Last Modified: 2023-10-31 11:35 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.