Hello Guys,
I would like to read out the smoke detector via SNMP using PRTG. For that, I need the OID to retrieve the data. Could someone help me and provide the OID? I have already tried to read the PowerNet MIB but without success. I would appreciate a response.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-05-18 11:13 PM . Last Modified: 2023-05-18 11:13 PM
Hi,
You can look into this table in the PowernetMIB.
memSmokeSensorStatusTable
.1.3.6.1.4.1.318.1.1.10.4.7.2