Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Problem after adding a new NetBotz

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Problem after adding a new NetBotz
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:59 PM . Last Modified: โ€Ž2024-04-03 11:42 PM

0 Likes
9
1520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:59 PM . Last Modified: โ€Ž2024-04-03 11:42 PM

Problem after adding a new NetBotz

Hi.

Yesterday I added a new NetBotz 570 to our DCE and it was correctly pubblished on the EcoStruxure APP. I can see all sensor but data are not visble (I see only a " - " near it). Graph data has been correclty reported.

 

If I click instead on an active incident inside the appliance I see:

 

and next after click on the device I see this:

 

In this last screen Network address and location of applianche disappear but data are displayed corretcly, also if I click on all sensor:

Instead starting from the dashboard if I open this device I cannot see all sensor data:

 

 

Can you help me on this?

Regards.

Davide

 

(CID:137107443)

Labels
  • Labels:
  • Data Center Expert
  • IT Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:59 PM . Last Modified: โ€Ž2024-04-03 11:42 PM

0 Likes
0
1521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:59 PM . Last Modified: โ€Ž2024-04-03 11:42 PM

Dear Davide Manassi,

Please, specify the version of the DCE software and the version of the Android mobile app?

With respect.

(CID:137107572)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:59 PM . Last Modified: โ€Ž2024-04-03 11:42 PM

0 Likes
0
1521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:59 PM . Last Modified: โ€Ž2024-04-03 11:42 PM

DCE is

Build client: 7.4.3.26

Build server: 7.4.3.26

Mobile APP instead is 1.0.69b1367

(CID:137107575)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 02:59 PM . Last Modified: โ€Ž2024-04-03 11:41 PM

0 Likes
0
1522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 02:59 PM . Last Modified: โ€Ž2024-04-03 11:41 PM

The fact is that I have the latest DCE-7.6.0 and Android mobile app v.1.0.69. And for my NetBotz-450 with T and TH sensors, I do not see such a problem...

(CID:137107583)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2024-04-03 11:41 PM

0 Likes
0
1522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2024-04-03 11:41 PM

We have two NetBotz 570 with same configuration, beacause one fails we change it with this new one.

We retain the old one because we want to check some parameter (we redefine entire configuration manually instead backup/restore it).

In the APP we see data from old NetBots correctly instead this new one report problem comunicated.

I think this an issue on the APP

(CID:137107597)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2024-04-03 11:41 PM

0 Likes
0
1522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2024-04-03 11:41 PM

Dear Davide Manassi,

I'm sure the problem is in the =SE= cloud, not in the mobile app or etc. Therefore, it is necessary to wait at least a day to verify this ๐Ÿ˜€.

With respect.

(CID:137107721)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2024-04-03 11:38 PM

0 Likes
2
1522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2024-04-03 11:38 PM

Hi.

i solve the issue. I removed the Struxure Ware Data Center Expert and installed and attache the Gateway Software (last release 1.4.3.9) that I installed on a Linux Centos Machine.

I have encontoured only some problem on display all sensor, I think that if you use more or 8 character in name of label in NetBotz appliance sensor are not correctly displayed on cloud app. I insert name that not excedd 8 char on lenght and all work fine. At last I have only a new question about how app display label but I will open a new thread for this.

Bye

(CID:137108072)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2024-04-03 11:38 PM

In response to DCIM_Support
0 Likes
0
1522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2024-04-03 11:38 PM

Dear Davide Manassi,

From your comments:

i solve the issue. I removed the Struxure Ware Data Center Expert and installed and attache the Gateway Software (last release 1.4.3.9) that I installed on a Linux Centos Machine.

I think the solution is to remove and register your DCE-server again. Check it out please.

I have encontoured only some problem on display all sensor, I think that if you use more or 8 character in name of label in NetBotz appliance sensor are not correctly displayed on cloud app.

However, I do not have a similar problem and I use a lot more than 8 characters in the sensor names of the NetBotz appliance:

With respect.

(CID:137108087)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2024-04-03 11:38 PM

In response to DCIM_Support
0 Likes
0
1522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2024-04-03 11:38 PM

Hi.

 

At this time I prefer to not make any other change on my configuration, this because I am not paied from Schneider to test its software (I am not a beta tester...). Also, this issue that I solved by myself affect production environment and all modification impact directly on our internal assurance service, to revert to Struxure Ware Expert publication I must schedule another downtime window and comunicate to techinician this outage.

 

I think that Schneider before release some update could test it better instead leaw all customer alone. But this is only my point of view.

 

Regards.

 

(CID:137108103)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2023-10-22 03:38 AM

0 Likes
0
1522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-05 03:00 PM . Last Modified: โ€Ž2023-10-22 03:38 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore