Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Physical Network connections (No API. ETL?)

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Physical Network connections (No API. ETL?)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
158
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
thombrooks
thombrooks
Explorer

Posted: ‎2024-12-06 04:04 PM

0 Likes
8
3479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-06 04:04 PM

Physical Network connections (No API. ETL?)

We are doing a proof-of-concept to help our support staff quickly locate end user workstations on a map. We already have the network jack locations mapped (in another third-party tool), and have CDP/LLDP info about which switch port each workstation is connected to. Since we already have an on-prem ITA instance, we figured we'd try using it as the source of truth for the 'missing link' - mapping switch ports to patch panel jacks.

 

After seeing this post, it appeared that the only way to retrieve or create physical network connections was by using ETL. We created an Export Internal job, applied the swoExportJob v2.0.0 transformation and set everything to 'true' (particularly 'Export network information.')

 

In the export database, we were able to traverse the network links between devices, patch panels, and switches by studying the configuration_item and configuration_item_relation tables.

 

However: we cannot seem to find a field containing the descriptions for a patch panel's module ports. This is important because it's how we track station cables (network jack numbers and letters.) To clarify - when we go to the properties of the patch panel, the 'Network' section, and the 'Back Connections' table, these ports do not have connections to other patch panels, but they do have the 'Description' defined with the station cable's jack number and letter. This is what we are trying to access.

 

Should we be able to see this information via ETL using the standard swoExportJob v2.0.0 transformation, or do we need to add to the default transforms in order to retrieve (and eventually add / update) these description fields?

 

Re: versions - server.log says DCE firmware version 8.0.0, ITA is 9.4.1.

 

Thank you!

Labels
  • Labels:
  • IT Advisor
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
gsterling
gsterling Mentor
Mentor

Posted: ‎2024-12-10 03:11 AM

0 Likes
2
3439
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-10 03:11 AM

Hello.

 

If you are trying to build your query via an ETL export database, then configuration_item and configuration_item_relation will identify connections beween objects. Port property info is part of the table relation_endpoint_property which should also be found in your ETL export database.

 

IT Advisor is expected to offer a REST api endpoint later in late 2025 to allow network queries as well as network features become more built out in the IT Advisor web client.

 

Regards

 

Greg Sterling

Reply

Link copied. Please paste this link to share this article on your social media post.

thombrooks
thombrooks
Explorer

Posted: ‎2024-12-10 10:30 AM

In response to gsterling
0 Likes
1
3415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-10 10:30 AM

Greg,

 

We are able to see the relationship between the switch port and the patch panel port. What we are not able to see is the contents of the 'End Port Description' field. That's the piece that connects us to our facility map.

 

Two of these screenshots are from the Network Cable Browser, which does show the info we're looking for.

The other screenshot is the only info we're able to see from the database tables: it's in Mod B, it's a regular RJ 45, it's not on the rear of the rack, and it's port # 21. 

 

Having done a sql dump of the entire ETL Export Database, searching for '4TRE-1185-A' or even '1185' yields no results.

 

Is this something we can add or modify to the ETL output transform so it will include these attributes?

 

Thank you!

 

Screenshot 2024-12-10 at 12.19.10 PM.pngScreenshot 2024-12-10 at 12.19.40 PM.pngScreenshot 2024-12-10 at 12.24.18 PM.png 

Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
gsterling Mentor
Mentor

Posted: ‎2024-12-12 03:47 AM

In response to thombrooks
0 Likes
0
3403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-12 03:47 AM

You are correct, the description field does not appear to be exported. We will capture a feature request to request this value is added to the export transformation.

 

Regards

 

Greg Sterling

Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
gsterling Mentor
Mentor

Posted: ‎2024-12-13 06:00 AM

0 Likes
2
3377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-13 06:00 AM

I have created feature request id EIAFR-680 for this item. Please note we cannot estimate a time when and if this request will be delivered. I will note ITA's network REST api's are expected to be improved in 2025 and some of these details will likely be included in that feature.

 

Regards

 

Greg Sterling

Reply

Link copied. Please paste this link to share this article on your social media post.

thombrooks
thombrooks
Explorer

Posted: ‎2024-12-18 11:37 AM

In response to gsterling
0 Likes
1
3325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-18 11:37 AM

We have created a modified version of the Network Endpoint Properties export transform (attached) and would appreciate it if your team could review. We plan to make the matching change on the input side next, and it would be good to know that we are following 'best practices' before we base that work on something that wasn't up to par. Thank you - TB 

 

Screenshot 2024-12-18 at 12.32.56 PM.png

 

Screenshot 2024-12-18 at 12.33.27 PM.png

 

Screenshot 2024-12-18 at 12.34.38 PM.png

 

Attachments
swoNetworkEndpointProperties_v2.0.0.ktr.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
gsterling Mentor
Mentor

Posted: ‎2025-01-03 06:44 AM

In response to thombrooks
0 Likes
0
3188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-03 06:44 AM

I have shared your transformation file. I cannot say with certainty whether any form of feedback will come back unless they decided to incorporate the change to ITA moving forward as they cannot promise a change made by a customer won't be impacted by other ITA changes or upgrades unless they are testing it themselves.

 

I should hear back from them in the next few business days.

Reply

Link copied. Please paste this link to share this article on your social media post.

thombrooks
thombrooks
Explorer

Posted: ‎2025-08-19 08:12 AM

0 Likes
1
1399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-19 08:12 AM

Following up on this thread. I know we have an upgrade coming up and am wondering if there has been progress on this API? Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
gsterling Mentor
Mentor

Posted: ‎2025-09-22 11:36 AM

In response to thombrooks
0 Likes
0
1257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-22 11:36 AM

Hello. Over the coming ITA releases there will be enhancements to network features in ITA's web client UI which should mean improvements to the network api's. The features are expected to be introduced over at least the next two ITA releases.

 

ITA 9.5.3 is expected in Oct 2025 which should include at least the ability to manage asset port configurations. The actual abilities to create/delete network connections in the web UI should come by the Feb 2026 release at which point I'd expect you'll see a more complete api offer for these features.

 

Regards

 

Greg Sterling

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore