Pelco cameras and Netbotz

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Pelco cameras and Netbotz
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:54 AM . Last Modified: ‎2024-04-08 02:44 AM

0 Likes
5
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:54 AM . Last Modified: ‎2024-04-08 02:44 AM

Pelco cameras and Netbotz

HI all, 

The list "http://www.schneider-electric.us/en/faqs/FA158450/" containing Pelco cameras tested with Botzware contains alot of cameras that reached end of sale and their part numbers are replaced in the market by other PNs.

So can any body please confirm if any of the below PNs are supported, please I urgently need your support

suggested models: IMP1110-1EI , IMP1110-1 & IXP11.

Thanks

Pierre

ITB NEA

(CID:110015691)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:54 AM . Last Modified: ‎2024-04-08 02:43 AM

0 Likes
3
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:54 AM . Last Modified: ‎2024-04-08 02:43 AM

Hi Pierre,

 

We try to keep k-base as up to data as possible but when it is not, release notes and other pages on the EcoStruxure IT Help Center site also note new features or supported items such as cameras or modems. As per this page:

What's new in NetBotz v4.5.4

There is only one new camera that is supported and that is:

  • Pelco Sarix IL 10

I do not see where the cameras in your query have been tested or are supported.

 

Thank you,

Steve.

(CID:110015748)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:54 AM . Last Modified: ‎2024-04-08 02:43 AM

0 Likes
3
1347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:54 AM . Last Modified: ‎2024-04-08 02:43 AM

Hi Pierre,

 

We try to keep k-base as up to data as possible but when it is not, release notes and other pages on the EcoStruxure IT Help Center site also note new features or supported items such as cameras or modems. As per this page:

What's new in NetBotz v4.5.4

There is only one new camera that is supported and that is:

  • Pelco Sarix IL 10

I do not see where the cameras in your query have been tested or are supported.

 

Thank you,

Steve.

(CID:110015748)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:54 AM . Last Modified: ‎2024-04-08 02:43 AM

In response to DCIM_Support
0 Likes
0
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:54 AM . Last Modified: ‎2024-04-08 02:43 AM

Hi Steven,

Thanks for the reply, however I guess I am miss understood here, all what I am saying is that the K-base contains obsolete part numbers so I have no confirmation that the equivalent new part numbers are supported !

Now I am stuck between these part numbers and dont know which to choose ? so what can I do here ?

IMP1110-1EI , IMP1110-1 & IXP11 ??

Thanks

Pierre

(CID:110015760)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:54 AM . Last Modified: ‎2024-04-08 02:43 AM

In response to DCIM_Support
0 Likes
0
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:54 AM . Last Modified: ‎2024-04-08 02:43 AM

Hi Pierre,

 

No, there was no misunderstanding. Although I am aware that these part numbers do become obsolete, they are THE  tested cameras. When new cameras are tested, it's usually in k-base immediately and should always be in the release notes. 

The fact that Pelco implies that these new cameras are the direct replacement for the old ones does not mean that they communicate exactly the same. Early in our integration attempt, we were under the impression that they all communicated the same way. We found that each camera and firmware had subtle differences....just enough so that we had to code for each individual camera. 

That being said, unless a camera model is specifically tested and listed as supported, we can not claim that it will work with the integration. The cameras you have listed have not been tested.

 

Steve 

(CID:110015794)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:55 AM . Last Modified: ‎2024-04-08 02:43 AM

In response to DCIM_Support
0 Likes
0
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:55 AM . Last Modified: ‎2024-04-08 02:43 AM

Thanks a lot dear Steve.

Regards

Pierre

(CID:110015812)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:55 AM . Last Modified: ‎2023-10-22 03:33 AM

0 Likes
0
1346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:55 AM . Last Modified: ‎2023-10-22 03:33 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore