Nuisance Netbotz Appliance timeout alarms in DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Nuisance Netbotz Appliance timeout alarms in DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:34 AM

0 Likes
8
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:34 AM

Nuisance Netbotz Appliance timeout alarms in DCE

Hi All,

 

With Netbotz 300+ appliances, in DCE the only way to receive an alarm notification if an appliance is unreachable or offline is via an email address configured to a specific user account whom has rights to view that particular appliance in DCE.

 

We have an issue with a particular site that due to network latency / network problems, frequently loses communication between the DCE server and Netbotz appliance - and this in turn triggers nuisance emails to all DCE account holders registered in the system.

 

Is there a way to set a time delay on these emails being triggered (in much the same way we can delay lost comms alerts through the Alert Profile for SNMP or Modbus devices)? - The client doesn't want to receive large numbers of spurious emails but does want to know if a device remains offline for an extended period of time.

 

Perhaps there is another way to achieve this that I am not aware of?

 

Many Thanks,

 

David

(CID:105470059)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:34 AM

0 Likes
2
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:34 AM

Hi David,

 

Sorry but there is no way to set any latency in the alarming of lost comms messages for NetBotz appliances in the 7.x versions of DCE. This has been a request in the past and I will forward this post to product management in the hopes that this may be addressed in a near future revision of 7.x. Just as an FYI, it is my understanding that future releases such as 8.x that support NetBotz will address this issue however that doesn't solve the immediate issue, I know. 

 

Thanks,

Steve

(CID:105470064)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:34 AM

0 Likes
2
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:34 AM

Hi David,

 

Sorry but there is no way to set any latency in the alarming of lost comms messages for NetBotz appliances in the 7.x versions of DCE. This has been a request in the past and I will forward this post to product management in the hopes that this may be addressed in a near future revision of 7.x. Just as an FYI, it is my understanding that future releases such as 8.x that support NetBotz will address this issue however that doesn't solve the immediate issue, I know. 

 

Thanks,

Steve

(CID:105470064)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:34 AM

In response to DCIM_Support
0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:34 AM

Thanks Steve

(CID:105470070)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:33 AM

In response to DCIM_Support
0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:33 AM

Welcome David... I both forwarded this to product management as well as added it to an already created enhancement request. Steve

(CID:105470071)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:33 AM

0 Likes
1
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:33 AM

Any updates on this?  I'm running 7.4.1.  I have a number of high latency satellite links I'm dealing with, and while I can control the APC equipment timeout warnings through SNMP settings in DCE I cannot for two NetBotz 570's that were recently put at the other end of those links.  It causing those objects in DCE to go red on a regular basis which our operations center staff are finding distracting.  It could be solved with timeout and retry option like with SNMP...

 

Thanks

-Steve

(CID:110020960)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:33 AM

In response to DCIM_Support
0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:33 AM

Good day

I am also receiving this issue.

Please keep me updated to any new developments or workaround solutions.

Kind regards

 

(CID:136644306)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:33 AM

0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:33 AM . Last Modified: ‎2024-04-09 12:33 AM

Hi Stephen,

 

Sorry but there is still no timeout or retries option available. You can slow the rate of communications down if that will help:

and when the device has an alert, it will contact DCE immediately.

I believe it takes 2 failed communications before the error is reported by DCE.

Keep in mind though that unlike SNMP that gets only the current value when polling, NetBotz sends all data since the last contact so that if it is gathering lots of data, doubling the poll rate will also likely double the data being sent. 

I know this was planned for 8.x but that too has been delayed. I will add your comments to the enhancement request.

 

Steve 

 

(CID:110790733)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:34 AM . Last Modified: ‎2024-04-09 12:33 AM

0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:34 AM . Last Modified: ‎2024-04-09 12:33 AM

Hi Stephen, David,

 

Just an FYI, I believe there is an automatic retries option that is not configurable. I'll verify this when I get some time but I am told there are 3 retries during the NetBotz communications loss. After my testing I'll still add this info into an enhancement request.


Steve

(CID:110790770)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:34 AM . Last Modified: ‎2023-10-31 11:27 PM

0 Likes
0
1448
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:34 AM . Last Modified: ‎2023-10-31 11:27 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore