Posted: 2020-07-05 01:58 PM . Last Modified: 2024-04-04 12:19 AM
Hi, two questions:
Question 1: is it possible to configure the y-axis max and min. In the graphic the max is 62.0 and min is 55.0 F. I would like the span to be min 40 and max 100 F.
Question 2: I note significant, unphysical temperature hysteresis (saw tooth waveform between 57.2 and 59.5). Is this typical ?
Thank you,
(CID:134696481)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 01:58 PM . Last Modified: 2024-04-04 12:19 AM
Dear nanoman,
Regarding your questions:
Question 1: is it possible to configure the y-axis max and min. In the graphic the max is 62.0 and min is 55.0 F. I would like the span to be min 40 and max 100 F.
As far as I know, this is not possible in APC AV software. You can try to make Feature requests, and maybe you will be heard.
Question 2: I note significant, unphysical temperature hysteresis (saw tooth waveform between 57.2 and 59.5). Is this typical ?
From my experience I will say, that it depends on the actual ambient temperature around the sensor. For example, such a temperature graph is very characteristic of server rooms where non-inverter cooling units are used (that is, when the compressor can either be turned on at 100% power or turned off altogether).
With respect.
(CID:137103312)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 01:58 PM . Last Modified: 2023-10-22 03:24 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.