Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Netbotz notificacion issue

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz notificacion issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:51 PM . Last Modified: ‎2024-04-03 12:40 AM

0 Likes
12
2724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:51 PM . Last Modified: ‎2024-04-03 12:40 AM

Netbotz notificacion issue

Hello team,

I have a problem with the email notifications of a Netbotz 250. I have a wireless sensor that is failing and we are receiving email notification every 2 minutes.

I have tried to disable this option for all the notifications from the menu Configure Actions for Groups of events:

but it does not work. It seems that it saves the changes but we are still receiving the emails every 2 minutes and if I enter again to check the configuration it appears with 2 minutes:

Then I have tried to change the specific parameters of this alarm, increasing the time between notification to one hour and only one repeat:

It appears properly configured:

 

But we are still receiving one email every hour, when it should be only 1 repeat:

 

Any idea?

(CID:148344061)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

Dear Javier, May I know the Netbotz appliance firmware which you are using? Can you please share us the config.ini file from NMC?

(CID:148344390)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

Hi Balaraman,

 

The firmware version is:

Firmware Revision
0.7.9
How can I download the config.ini file?
Regards

 

 

(CID:148766722)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

Hello Balaraman,

I have found how to download the config.ini file:

config.ini

Regards

(CID:148766734)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

Javier Zurera Hi Javier, Sorry, I can not download the config.ini. I see "attachment deducted" message. You can find the appliance firmware version on its NMC web interface under About-Network. Please make sure that the application module and AOS are up to date. 

Go to this below web URL and select NetBotz Security and Environmental Monitoring

https://www.apc.com/in/en/tools/download/index.cfm

You can notice that NetBotz Firmware v6.6.7 is the latest version. If your appliance version is not up to date, then I request you to upgrade the firmware and check if the email settings work as per your configuration. 

The procedure to upgrade Netbotz 250 can be found in the below link:

https://www.apc.com/us/en/faqs/FA299748/

Regarding your actual wireless sensor communication issue, here are my recommendations to improve the wireless sensors performance.

Please upgrade the NBRK0250 appliance firmware to the latest version(version6.6.7), and also upgrade the Wireless Sensors firmware versions to the latest firmware version.
You can upgrade the wireless sensors firmware by using the Wireless sensors firmware upgrade utility. 

Once the firmware upgrade of the appliance and wireless sensors are done, it is important to verify the RSSI signal levels of the Wireless sensors.
In my opinion, the RSSI signal is one of the key factors for the Wireless sensors to have a proper communication with Appliance. I always recommend the RSSI signal to be higher than 80 % level to avoid inactive issues. 

The poor RSSI signal strength will cause the sensors to go on or off the network. This will eventually cause the battery of the wireless sensors to go faulty.

So it is important you review the wireless sensors position, coordinator position and router(if available) positions in the data center. One of the good ways to improve the signal strength is to place the Routers to the outside of the top of racks by using USB extender cable.

Upgrade firmware on all NBWC100U wireless coordinators and routers to version 1.1.1 or higher.

Upgrade firmware on all NBWS100T/H wireless sensors to version 1.1.2 or higher.

Follow the instructions in the readme.txt file that is included in the utility to know the procedure to upgrade the firmware of wireless sensors using the utility.
or

You can refer https://sxwhelpcenter.ecostruxureit.com/display/public/UANB250/NetBotz+Wireless+Sensor+Update+Utilit...

I also written a tip in which you can find procedure to upgrade the wireless sensors firmware.
https://community.ecostruxureit.com/questions/122691506/procedure-to-update-the-netbotz-wireless-sen...

The NetBotz Wireless Sensor Update Utility build v102-05 is attached here netbotzwirelessutilitysetup_v102-05.zip which includes the latest wireless sensor fw. 

I hope this helps. 

(CID:148766750)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

Hi Balaram,

I have checked the firmware version and we are not in the latest version. We are going to try to update the firmware.

Regarding the wireless sensors, we have the same problem with the wired sensors. Every alarm that is trigered on, it sends emails every 2 minutes, and we have configured all the alarms with no repeat.

 

(CID:148766776)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

Javier Zurera Hi Javier, please upgrade to the latest firmware version and see if it works fine. If there is any issue, please let me know. Thanks!

(CID:148766786)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

Hi Balaraman,

I have updated the Netbotz with the Firmware Upgrade Utility but I have now the same version as before, v.6.5.6. I upgraded the Netbotz when we installed it one month ago. But we don't get the latest firmware v6.6.7 as you mentioned:

 

 

(CID:148766806)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

It is strange to see that the firmware is same after upgrade. Are you using the correct firmware executable file of 6.6.7? I suggest to delete the file that you downloaded already and try to download the Network Management Card v6.6.7 NB250 Firmware Executable file, and then try to upgrade. 

(CID:148766813)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:40 AM

Hi Balaraman,

I only see these options:

 

(CID:148766818)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:39 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:52 PM . Last Modified: ‎2024-04-03 12:39 AM

Dear Javier,

Can you please filter by Filter By Software / Firmware, and then select NetBotz Security and Environmental Monitoring?

or

Try this link here.

Regards,

Bala

(CID:148766880)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:53 PM . Last Modified: ‎2024-04-03 12:39 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:53 PM . Last Modified: ‎2024-04-03 12:39 AM

Thank you Bala,

with your link I could update the Netbotz to version 6.6.7

I will monitor the notifications with this new firmware.

 

(CID:148766903)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:53 PM . Last Modified: ‎2023-10-22 03:24 AM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:53 PM . Last Modified: ‎2023-10-22 03:24 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.