Netbotz Wireless NBWC100U disabled

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz Wireless NBWC100U disabled
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:11 AM . Last Modified: ‎2024-04-09 12:41 AM

0 Likes
6
1073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:11 AM . Last Modified: ‎2024-04-09 12:41 AM

Netbotz Wireless NBWC100U disabled

Hi guys, 

My customer has a Netbotz Wireless NBWC100U connected to a Netbotz 570 and some times it is disabled. To enable again I need to reset the Netbotz 570 and disconnect and connect the USB.

How can I avoid this problem?

Best regards,

 

Enric

 

(CID:105468746)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:11 AM . Last Modified: ‎2024-04-09 12:41 AM

0 Likes
3
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:11 AM . Last Modified: ‎2024-04-09 12:41 AM

Hi Enric,

 

I've not seen that happen before. Let's check on a few things.

What firmware are you running on the NBRK0570?

What firmware does it show for the wireless coordinator?

You do have only one of these connected to the unit, correct?

You said you disconnected it and reconnected it, did you try installing it to a different USB port to rule out a port issue?

How long does it take to show up as disconnected? 

How many other sensors and pods (wired or wireless) are connected to this unit? If you connect only the coordinator for a test, does the issue still occur?

If you go to the wireless sensor setup, what exactly do you see?

 

Before the next occurrence of the issue, go into advanced view and change the logging levels. Change the global level to alert so you only get very few messages from other components. Set the wireless to informational or trace so you get the most info. 

 

The next time the issue occurs, grab the logs from:

http:///cgi-bin/nbSupportCGI?cmdid=logread


Steve

 

 

(CID:105468750)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:11 AM . Last Modified: ‎2024-04-09 12:41 AM

In response to DCIM_Support
0 Likes
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:11 AM . Last Modified: ‎2024-04-09 12:41 AM

Hi Steve,

The firmware running on the NBRK0570 it's the latest, 4.5.1.
How can I see the wireless coordinator firmware version?
I only have one wireless coordinator connected to the Netbotz 570.
I don't tried to connect the wireless coordinator to other USB port.
The wireless coordinator has been showed up as disconnected some weeks after the connection.
The Netbotz 570 has a lot of wired sensors and pods, about 50 sensors and 10 pods and we cannot connect only the wireless coordinator so the problem is happening after some weeks and we cannot have the other sensors unpluged.

When I go to the sensors, they are with grey color (unavailable) and show the value N/A.


I will change the level log and when it will occur again I'll send you the logs.

Best regards,

 

Enric

 

(CID:105469145)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:11 AM . Last Modified: ‎2024-04-09 12:41 AM

In response to DCIM_Support
0 Likes
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:11 AM . Last Modified: ‎2024-04-09 12:41 AM

Hi Enric,


To find the firmware, you need to go to the wireless sensor setup. Here's an example:

Since there are no batteries in the coordinator it is pulling power from the unit. With 10 pods, I'm wondering if there is a power issue. Do you have any power supplies connected to any of the sensor pods? Can you remove all the other sensors and reboot the device to see if the wireless coordinator is re-discovered? 


How long does it take for the coordinator to show disabled / disconnected? Are the wired sensor pods A-link or USB? Is the coordinator connected directly to the unit?


Steve

(CID:105469146)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:11 AM . Last Modified: ‎2024-04-09 12:41 AM

In response to DCIM_Support
0 Likes
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:11 AM . Last Modified: ‎2024-04-09 12:41 AM

Hi Steve, I've seen the firmware version as you can see in the attached screen shot. It's needed to upgrade or it's right? Anyway, the customer has just 8 pods connected with any additional power suply and we cannot do the trial you suggest. The coordinator is directly connected to the Netbotz 570, not to a pod. Regards, Enric

Captura.JPG

(CID:105469514)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:12 AM . Last Modified: ‎2024-04-09 12:41 AM

0 Likes
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:12 AM . Last Modified: ‎2024-04-09 12:41 AM

Hi Enric,

If you have 5.4.1, the coordinator should upgrade to 1.0.3. It is possible that because it loses communications, it's not getting upgraded. Apparently your wireless sensors are not updating either.

It is possible that you have a faulty unit or coordinator and attaching the coordinator to another USB port would at least rule out a bad port on the unit but you have not tried that as per your statements above. If you can't run tests and troubleshoot, there's very little I can help with. I've seen no logs so if there is something happening on the bot that is causing this, I can't see it. I do understand that if the issue occurs only after a few weeks that it is difficult to troubleshoot but it is also difficult to suggest other options for troubleshooting.

You can try contacting tech support but before replacing any of the components, they will likely suggest similar troubleshooting steps before potential component replacement. I've not seen this issue before and it's likely that those that you would speak with in support have not either.

 

The only other options that I can see is that if you have other systems with similar setups, swap out the coordinators. At that point, if you have the issue again, you can at least see if it follows the coordinator or the NetBotz appliance.

 

Steve.

 

 

(CID:105469518)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:12 AM . Last Modified: ‎2023-10-31 11:27 PM

0 Likes
0
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:12 AM . Last Modified: ‎2023-10-31 11:27 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore