Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Netbotz Generate New Self-Signed Certificate

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz Generate New Self-Signed Certificate
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

0 Likes
11
3343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

Netbotz Generate New Self-Signed Certificate

Is there a way to generate a new self-signed certificate for our Netbotz 450 appliances.  They are running v 4.6.2 firmware.  The current certificate for the Netbotz listed in our DCE has expired.  Thanks.

(CID:132654566)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

0 Likes
9
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

Dear Sean Riley,

First, you need to make sure that your NetBotz-450 uses a valid self-signed certificate for communication over the HTTPS protocol.

  • If this is the case, you simply need to open the NetBotz-450 web-GUI in any browser and export the self-signed certificate to a plain text file in a standard way. Then you can import this self-signed certificate from a plain text file into the DCE-server in the standard way.
  • If this is not the case, i.e. NetBotz-450 has invalid self-signed certificate, then you can try to just reboot it. During the initial boot NetBotz-450 will determine its own invalid self-signed certificate and perform its automatic regeneration by default. The same process occurs when you disable the HTTPS port and re-enable it in the APC Advanced View Web Server Configuration settings.

Try and tell please the result.

With respect.

(CID:132654717)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

0 Likes
9
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

Dear Sean Riley,

First, you need to make sure that your NetBotz-450 uses a valid self-signed certificate for communication over the HTTPS protocol.

  • If this is the case, you simply need to open the NetBotz-450 web-GUI in any browser and export the self-signed certificate to a plain text file in a standard way. Then you can import this self-signed certificate from a plain text file into the DCE-server in the standard way.
  • If this is not the case, i.e. NetBotz-450 has invalid self-signed certificate, then you can try to just reboot it. During the initial boot NetBotz-450 will determine its own invalid self-signed certificate and perform its automatic regeneration by default. The same process occurs when you disable the HTTPS port and re-enable it in the APC Advanced View Web Server Configuration settings.

Try and tell please the result.

With respect.

(CID:132654717)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

In response to DCIM_Support
0 Likes
0
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

Additionally if you have a valid self signed cert but simply want  a new one, go to configuration–>network settings. Change the hostname and reboot. A new cert will be created. You can then change the hostname back again (and get another new cert).

 

Steve

(CID:132654985)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

In response to DCIM_Support
0 Likes
0
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

Thanks for the information.  Much more helpful than what I found in my searching. 

Does the self signed certificate need to be expired before it will perform the automatic regeneration of the self-signed cert?  Or will it regenerate if say there is a month left on the cert?

Thanks.

 

(CID:132659452)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

In response to DCIM_Support
0 Likes
0
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

Hi Sean, Simply changing the hostname or even the NetBotz time will regenerate a cert. This will happen regardless of the cert's current status / validity.

 

(CID:132654992)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

In response to DCIM_Support
0 Likes
0
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

Dear Sean Riley,

Does the self signed certificate need to be expired before it will perform the automatic regeneration of the self-signed cert?  Or will it regenerate if say there is a month left on the cert?

The self-signed certificate for NetBotz-4.x appliance is created for five years, and so far I can not say anything on this issue...

With respect.

(CID:132659450)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

In response to DCIM_Support
0 Likes
0
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:16 PM

Tried changing the time, but the cert is still the same.  Rebooted as well after changing the time.  I was avoiding changing the host name as I was not sure if DCE would like that.

(CID:132655038)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:15 PM

In response to DCIM_Support
0 Likes
0
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:17 PM . Last Modified: ‎2024-04-04 11:15 PM

Maybe time zone, I can test but don’t recall. Again, change the hostname and upon reboot, change it back. DCE should have no issue and you can also take it offline to do so. 

 

Steve. 

(CID:132655048)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:18 PM . Last Modified: ‎2024-04-04 11:15 PM

In response to DCIM_Support
0 Likes
0
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:18 PM . Last Modified: ‎2024-04-04 11:15 PM

Tried changing the time, but the cert is still the same.  Rebooted as well after changing the time...

So it should be, because changing time is a bad idea... It seems to me, that if you can reboot the NetBotz-450, then you can perform the self-signed certificate regeneration as it is written above in the answer.

With respect.

(CID:132655058)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:18 PM . Last Modified: ‎2024-04-04 11:15 PM

In response to DCIM_Support
0 Likes
0
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:18 PM . Last Modified: ‎2024-04-04 11:15 PM

My Netbotz self-signed certs expire next month.  So they are still valid.  I was trying to be proactive in getting them updated, rather than waiting for them to expire.  I wish there was more detail on installing our own trusted certs from our MS CA, but reading through the documentation I could find, made it seem quite cumbersome.

(CID:132655106)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:18 PM . Last Modified: ‎2024-04-04 11:15 PM

In response to DCIM_Support
0 Likes
0
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:18 PM . Last Modified: ‎2024-04-04 11:15 PM

Dear Sean Riley,

...I wish there was more detail on installing our own trusted certs from our MS CA, but reading through the documentation I could find, made it seem quite cumbersome.

But if everything is done correctly according to the documentation, then you will get an excellent result 😀.

  • To help you, I recommend you read the instruction Creating a Certificate Signing Request (CSR) for NetBotz-4.x appliances.
  • In addition, a small utility APC Network Management Card Security Wizard v1.0.4 can be very useful.
  • And in addition to this topic, there are two small documents Security Handbook for APC Network Management Cards AOS v5.x.x and Security Handbook Network Enabled Devices AOS V.6.5.X that will help you avoid mistakes and inaccuracies.

I hope this helps you.

With respect.

(CID:132655392)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 07:18 PM . Last Modified: ‎2023-10-22 03:22 AM

0 Likes
0
3341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:18 PM . Last Modified: ‎2023-10-22 03:22 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore