Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Netbotz And Sensor Not Working

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz And Sensor Not Working
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:32 PM

0 Likes
8
3468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:32 PM

Netbotz And Sensor Not Working

I have Netbotz Rack Monitor 450 and AP9520TH Temp Sensor that connect to Rack Monitor with A Link Port but there is nothing show in Netbotz Appliance and not Detect Sensors Automatically . I Test the firmware 4.5.4 and 4.6.2 both . 

(CID:132647169)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

0 Likes
2
3467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

Hello, 

Per Steve's note, what is the serial number on the AP9520TH, or what are the first 4-6 letters/numbers?

Does the AP9520TH display information when connected to the Netbotz?  As long as it is connected to a Netbotz unit that is powered on, then it should power on and report the firmware revision as it (the AP9520TH) boots.  If it does power on, what does it display?  If it doesn't power on, then I would try different network cables, or if possible other Netbotz devices.

If the AP9520TH display shows information after it is powered, then the most likely cause is either an incorrect connection or dipswitch configuration.  If there are multiple AP9520TH's connected, did you configure the dipswitches prior to powering them?  If not, then I would disconnect all physical connections, both network and power.  Once all are powered off I would configure the dipswitches (per Bala's note).  Once configured, I would power all equipment back on and confirm that they work.

Thanks.

(CID:132647208)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:32 PM

0 Likes
1
3467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:32 PM

Dear Zahramnejad,

Please refer the below post on how to connect AP9520TH to the Netbotz Appliance A-Link. There is a dip switch setting that needs to be set correctly. The below post is related to 250, but it is applicable for AP9520TH that dip switch settings need to be verified. 

Installing a temperature/humidity sensor with display (AP9520TH)

 

  • Make sure that the power cable/ethernet/anything else are disconnected from the Netbotz 450 and that all Cat5 and terminators are disconnected from the AP9520TH sensors.  
  • There should be no physical connections at the Netbotz 450 (power/ethernet/anything) or the AP9520TH (Alink terminator).
  • Once all are disconnected, set the dipswitches on each AP9520TH to off (Setting 1 - see below), and connect to the appliance.   At this time, power on the Netbotz 450.  When powered on, check if the sensor is recognized. 



I hope this helps.

Regards,

Bala

(CID:132647176)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:32 PM

In response to DCIM_Support
0 Likes
0
3467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:32 PM

I did it, but it doesn't work

 

(CID:132647846)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

0 Likes
1
3467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

Hi,

Do you have other sensors or pods connected to the Alink port?  

What is the serial number ( at least first 6 characters) of the attached sensor?

Are you using a ca 6 or 5 cable. Cat 5 should be used. 

Do you have any other sensors, pods, or NetBotz to test with?

What are the dip switch settings? I believe they should all be down if this is going to be  the first in line. If you have multiple Alink sensors connected, make sure they have unique dip switch codes. 

 

Thanks,

Steve. 

 

 

(CID:132647188)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

In response to DCIM_Support
0 Likes
0
3467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

ZA1422004933 = Serial num

Dont Have any pods.

No Dont have Any Other Netbotz

i try to use only one sensor so i think dipswitch doesnt matter correct ? 

(CID:132647502)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

0 Likes
2
3468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

Hello, 

Per Steve's note, what is the serial number on the AP9520TH, or what are the first 4-6 letters/numbers?

Does the AP9520TH display information when connected to the Netbotz?  As long as it is connected to a Netbotz unit that is powered on, then it should power on and report the firmware revision as it (the AP9520TH) boots.  If it does power on, what does it display?  If it doesn't power on, then I would try different network cables, or if possible other Netbotz devices.

If the AP9520TH display shows information after it is powered, then the most likely cause is either an incorrect connection or dipswitch configuration.  If there are multiple AP9520TH's connected, did you configure the dipswitches prior to powering them?  If not, then I would disconnect all physical connections, both network and power.  Once all are powered off I would configure the dipswitches (per Bala's note).  Once configured, I would power all equipment back on and confirm that they work.

Thanks.

(CID:132647208)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

In response to DCIM_Support
0 Likes
0
3467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

ZA1422004933 Is Serial

-Yes It display the information when connectet on the sensor but not recognize by netbotz appliace

-I Tried Different Network Cable

-yes i have more than one sensor BUT i try to connect only one sensor and i dont think it need dipswitch configuration for one sensor am i right?

 

 

 

(CID:132647498)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

In response to DCIM_Support
0 Likes
0
3467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:27 PM . Last Modified: ‎2024-04-04 11:31 PM

Hello,  if the display is functional when you connect over the Alink port then it would appear that the sensor is working.  When it powers on, what does it report on the display?

Any of the dipswitch settings outlined in the install guide should work, though I would set all four to "Off" (Config 1) if you still cannot get the sensor to communicate with the Netbotz device. 

I would make sure to power off the Netbotz device, disconnect all network cables from both the Netbotz and sensor(s) or additional sensor pods, make sure the sensor dipswitches are set in a way unique from any other sensors (if only 1 sensor is connected then all "Off" may be good), and then reconnect power then Alink power.  If it is still not working then Alink comm does not sound like it is working, which could be at the Netbotz or the sensor.  If you have another Netbotz or sensor to test with, I would do so and try to determine which device is not working. 

 

Based on the serial number the sensor is out of warranty, unless you have a proof of purchase showing it was purchased within the last 2 years.

(CID:132649264)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 06:28 PM . Last Modified: ‎2023-10-22 03:22 AM

0 Likes
0
3467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:28 PM . Last Modified: ‎2023-10-22 03:22 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore