Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Netbotz 750 Camera NBPD0165 Surveillance clips Can't store in DCE Serv

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz 750 Camera NBPD0165 Surveillance clips Can't store in DCE Serv
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:14 PM . Last Modified: ‎2024-04-03 12:12 AM

1 Like
4
2849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:14 PM . Last Modified: ‎2024-04-03 12:12 AM

Netbotz 750 Camera NBPD0165 Surveillance clips Can't store in DCE Serv

Hi Support Team,

There is a customer installed a AP9465 and a Netbotz 750 with 4 NBPD0165 cameras,ther want  view  all of the camera's surveillance clips through the DCE,as the Netbotz 750  can only save the last 96  hours Surveillance clips.  But there is no Surveillance clips in the DCE Server,Why?

DCE  : AP9465 for Server Build: 7.7.0.148

Netbotz 750:  Build_5.2.0.3061

Surveillance configuration: 10 or 5frames per second and a resolution of 800x600. 

(CID:151062431)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:14 PM . Last Modified: ‎2024-04-03 12:12 AM

0 Likes
2
2850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:14 PM . Last Modified: ‎2024-04-03 12:12 AM

Dear Mamacoo,

Were you able to discover the Netbotz 750 appliance in DCE software successfully? 

Do you see any error message in DCE active alarm for this device? 

I suspect that you may have this error. If you have this error, please follow the below steps to resolve this error, and then see if you are able to see the cameras in DCE, and then apply the DCE surveillance license. 

Ensure the device has a valid SSL certificate, and add the certificate to the list of trusted SSL/TLS certificates if not signed by a trusted root authority. Alternatively, set the SSL/TLS certificate verification to a less strict option by following the below steps.

In Netbotz UI-

1. Navigate to Settings< System

2. Go to Settings > System > DCE Surveillance and uncheck "Verify DCE Certificate in Trust Store"

 

In DCE:

1. In DCE discover NB750 using v1/v3(Whichever is configured in Netbotz UI)

 

2. Go to Device > NetBotz Appliance Communication Settings > NetBotz Appliance Credentials > (add the Netbotz UI login credentials)

 

3. Go to Device > NetBotz Appliance Communication Settings > NetBotz 750 Camera Communication Settings > (check the Bot by Ip) >

Edit Communication Settings > Check Use SSL, Set port to 443, SSL Verify Options: No verification*

 

As you can see in the below screen shot, I can see the camera pod 165 of Netbotz 750 appliance in DCE software, and I can see the stored clips in DCE after I click on Retrieve clips option.

(CID:151062484)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:14 PM . Last Modified: ‎2024-04-03 12:11 AM

In response to DCIM_Support
0 Likes
0
2851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:14 PM . Last Modified: ‎2024-04-03 12:11 AM

 Hi Balaraman,

This guide solved my problem,Thank you!

(CID:151063664)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:14 PM . Last Modified: ‎2024-04-03 12:11 AM

In response to DCIM_Support
0 Likes
0
2851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:14 PM . Last Modified: ‎2024-04-03 12:11 AM

Dear mamacoo Thanks a lot for the update. I am glad that your issue is resolved. Please accept the answer so that this post can also help other users who face this similar issue. 

(CID:151063666)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 11:14 PM . Last Modified: ‎2023-10-22 03:21 AM

0 Likes
0
2851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:14 PM . Last Modified: ‎2023-10-22 03:21 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore