Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Netbotz 570 pod unplugged

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz 570 pod unplugged
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

0 Likes
6
2116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

Netbotz 570 pod unplugged

Hello.

We actually have the following issue at Netbotz Portal:

We have checked every devices of the screenshot and no one has any alarm.

This is a new installation in a costumer.

We have seen that there are some similar cases, but are dated from 2016.

We need some advice or the confirmation that this bug is still unsolved to inform our costumer.

Thank you.

Regards.

(CID:138812511)

Labels
  • Labels:
  • NetBotz
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

Hi Alvaro,

The screenshot is not displaying well so I really can't see the messages. I can't tell which pod is unplugged. I am also unaware of any "bug" of this type. 

If this is the internal pod, I suggest disconnecting all sensors and external pods then, following k-base FA176133, re-flash the firmware on the 570. Do not use the "rootupgkeep" option.

After you're finished, if the integrated pod is still listed as unplugged, it is likely a hardware issue and the unit should be replaced.

If it works fine after the re-flash, be conscious of how you reconnect everything and if it happens again, note what you did that may have caused it. Perhaps a wrong connection, too many external pods without external power, perhaps a bad external pod, sensor, or cable, etc. 

If it's a different pod that is erring, I would do some of the same troubleshooting as above...disconnecting and reconnecting different pods until you find what's causing it.


As for your comment:

We have checked every devices of the screenshot and no one has any alarm.

I don't understand what you're trying to say here. 

You show a screenshot of a 570 and there are some alarms (as I mentioned, I can not read them) .  I can tell they are in what appears to be Spanish but I can't even see most of the letters to be able to use google translate. I can only tell there are alarms. Perhaps a better screenshot and perhaps in English.  Is the alarm not listed here? If not, where are you seeing the alarm? If you look under the pods, are they in error? Perhaps looking in Advanced View will show you better what's happening. 


Steve




 

(CID:138812574)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

Hi Alvaro,


Is the Netbotz installed with 5 node monitoring license? What I can tell is that the unplugged devices are PDU, UPS, and InRow. 

Have you checked the network connection status between Netbotz and the monitored devices? 


Best Regards, 


TJ

(CID:138812709)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

0 Likes
0
2116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

Dear Álvaro González Jouve,

Tell us, please, did you solve your problem or not?

With respect.

(CID:139693909)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

0 Likes
0
2116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

Yes, today we've deleted all the external pods of the netbotz database, and now there're no error messages in the netbotz appliance.

The problem was that our netbotz had all the devices registered with the old IP assignation. 

We have a DCE so we don't really need that netbotz discovered other devices of the Smartbunker.

Thank you.

(CID:140215999)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

0 Likes
0
2116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:45 PM . Last Modified: ‎2024-04-03 04:23 AM

Ok, very thanks for the good feedback 😀.

(CID:140216036)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:46 PM . Last Modified: ‎2023-10-22 03:21 AM

0 Likes
0
2116
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:46 PM . Last Modified: ‎2023-10-22 03:21 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore