Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Netbotz 355 no longer works after trying to update firmware

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz 355 no longer works after trying to update firmware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:53 PM . Last Modified: ‎2024-04-04 12:21 AM

0 Likes
8
2451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:53 PM . Last Modified: ‎2024-04-04 12:21 AM

Netbotz 355 no longer works after trying to update firmware

Using AV I attempted to update firmware. The Botz no longer responds to AV or serial configuration utility. I was able to use serial port (via hyperterminal) to get into Botz. Tried to upgrade firmware using TFTP but no joy (see issue on Botz 455).  Can I update the firmware through the serial port ?  If so, how? Although I can setenv IP Addr / IPmask / IPgateway  it appears that the botz is not recognized by network.

I am hoping the Botz can be brought back to life.

Thank you,

Scanning JFFS2 FS: ....................... done.

drwxr-xr-x 0 Tue Oct 31 18:45:36 2017 bin
drwxr-xr-x 0 Tue Oct 31 19:07:24 2017 dev
drwxr-xr-x 0 Tue Oct 31 19:07:24 2017 etc
drwxr-xr-x 0 Tue Oct 31 18:45:36 2017 lib
drwxr-xr-x 0 Tue Oct 31 19:07:23 2017 mnt
drwxr-xr-x 0 Tue Oct 31 19:07:23 2017 opt
drwxr-xr-x 0 Fri Dec 13 19:15:32 2013 sys
drwxrwxrwt 0 Sun Nov 11 01:18:25 2018 tmp
drwxr-xr-x 0 Mon Apr 04 16:41:39 2016 usr
drwxr-xr-x 0 Mon Apr 04 16:42:00 2016 var
-rw------- 1024 Thu Jan 01 00:26:53 1970 .rnd
drwxr-xr-x 0 Fri Feb 28 18:13:17 2003 home
drwxr-xr-x 0 Fri Feb 28 18:13:17 2003 proc
drws------ 0 Mon Apr 04 16:41:33 2016 root
drwxr-xr-x 0 Mon Apr 04 16:41:39 2016 sbin
drwxr-xr-x 0 Tue Oct 31 18:45:41 2017 cramfs
lrwxrwxrwx 11 Sun Nov 11 01:22:24 2018 linuxrc -> bin/busybox
-rw-r--r-- 1280558 Tue Oct 31 19:07:33 2017 nbKernel
drwx------ 0 Fri Dec 13 19:38:12 2013 lost+found

Loading NetBotz Data Modules...
insmod: /opt/netbotz/cbin/modules/nbWatchdog.ko: No such file or directory
ERROR: major number for nbWatchdog not found
insmod: /opt/netbotz/cbin/modules/nbVariables.ko: No such file or directory
ERROR: major number for nbVariables not found
ERROR: major number for nbVariables not found
ERROR: major number for nbVariables not found
/opt/netbotz/initterm/earlyinit/37_nbvarinit: /opt/netbotz/initterm/earlyinit/37
_nbvarinit: 106: /opt/netbotz/bin/nbhwclock: not found
/opt/netbotz/initterm/earlyinit/37_nbvarinit: /opt/netbotz/initterm/earlyinit/37
_nbvarinit: 106: /opt/netbotz/bin/nbhwclock: not found
insmod: /opt/netbotz/cbin/modules/nbClock.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbErrorCond.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbUser.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbEnclosure.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbSensors.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbDIN.ko: No such file or directory
ERROR: major number for nbDIN not found
insmod: /opt/netbotz/cbin/modules/nbDINAnalog.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbDINAmpDetect.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbDINDryContact.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbRelayOut.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbRelayOutSwitch.ko: No such file or directory

insmod: /opt/netbotz/cbin/modules/nbRelayOutOutlet.ko: No such file or directory

insmod: /opt/netbotz/cbin/modules/nbRelayOutButton.ko: No such file or directory

insmod: /opt/netbotz/cbin/modules/nbCamera.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbAudio.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbProcFiles.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbLicense.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbFileObj.ko: No such file or directory
insmod: /opt/netbotz/cbin/modules/nbPseudoPod.ko: No such file or directory
ERROR: major number for nbPseudo not found
/opt/netbotz/initterm/earlyinit/37_nbvarinit: /opt/netbotz/initterm/earlyinit/37
_nbvarinit: 120: cannot create /proc/nbvar/nbkmsg: Directory nonexistent

(CID:134695948)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

0 Likes
6
2451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

hello nanoman,

I have same problem with NetBotz 355, in Brazil support say "have no repairing, buy another netbotz"

but this is a software problem, and in Brazil netbotz have high price. then I think upgrade firmware by console. I found this link below and netbotz "re-born" after firmware update.

 http://www.apc.com/us/en/faqs/FA176133/

 

try do this and sey if working.

 

see you

Lucinei Junior

(CID:135432004)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

In response to DCIM_Support
0 Likes
0
2451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

Ref: APC FAQ    http://www.apc.com/us/en/faqs/FA176133/

Hi Thanks for the response. As I alluded to in my write up/question (see issue on 455), I tried the console firmware update using TFTP.  But I get the error described in FAQ "T T T T T".

Below is my setup: I am using a laptop into a stand alone router (no firewall).

                USB cable between laptop and Botz  - computer running hyperterminal

                Running TFTP.  

I can console in and set env parameters.  When I print the env they appear to be set.

Attempt to update firmware via issuing postupg but get the error described in FAQ (.. means the network is not setup correctly...). I have checked the TFTP setting and they see to be correct and pointing to the correct directory.

            The botz is displaying temperature and the Ethernet led is illuminated.

ASIDE: after I set the botz IP address it still is not recognized by router ?

Did you perform a console update and did it work ?

Any ideas or help will be appreciated.

Thanks.

(CID:135432312)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

In response to DCIM_Support
0 Likes
0
2451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

hello

the firmware files are on TFTP without folder?
I try with solarwinds TFTP and receive " T T T T" error too
then I try with TFTP32D, because I can see transfer on TFTP32D in realtime. and this work

I think windows 10 blocking solarwinds TFTP.

end if you can see IPs corret by console with comand "printenv", Netbotz accept configuration. don't forget to ussing "saveenv" to save IP configuration.

see you

(CID:135432333)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

In response to DCIM_Support
0 Likes
0
2451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

hey, I try do same in Netbotz 570.

 

Firmware update run normal. but don't work. then I enter by console again and run comand "configreset" to reset configuration. after boot netbotz 570 re-born too

 

see you 

(CID:135432345)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

In response to DCIM_Support
0 Likes
0
2451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

Thanks for the clue/path on solarwinds TFTP. 

I downloaded and installed TFTP32D (64 install). it throws a "Bind error 10013 An attempt was made...." see image.

http://tftpd32.jounin.net/

 

See network setup in earlier comment. 

As far as setting up the TFTP server, only selected the TFTP server and the path where bin file is. Does not work.  Any ideas or thoughts will be appreciated.

Tftp64: Settings:  TFTP only

 

Tftp setting:

Directory of Botz Firmware

 

 

(CID:135432980)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

In response to DCIM_Support
0 Likes
0
2451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

I should have added. I did follow in the instructions per guide located at:

http://www.tricksguide.com/how-to-setup-a-tftp-server-tftpd32-windows.html

(CID:135432990)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

In response to DCIM_Support
0 Likes
0
2451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2024-04-04 12:21 AM

hi

it's strange, I use portable version and run by admin (right click "Run as administrator") I put files on disk "C:\TFTP-Root" because maybe administrador don't have access on user folder.

and about TFTP32D configurations, I just disabled DHCP Server, see imagens

try click em "Show dir" you can see Firmware files?

 

 

 

see you

(CID:135433004)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2023-10-22 03:18 AM

0 Likes
0
2451
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 01:54 PM . Last Modified: ‎2023-10-22 03:18 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore