Netbotz 200 SNMP

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz 200 SNMP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

0 Likes
5
1407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

Netbotz 200 SNMP

We have a Netbotz 200 and i'm trying to allow a NMS system to read its SNMP.

 

I've told the NMS in question (whatsupgold) to use only a specific SNMP group credentials for the netbotz.

 

However whenever i then scan the netbotz i get alarms stating an unauthorized user tried to access SNMP on the the netbotz.

 

Can anyone assist me with this.

(CID:105456888)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

0 Likes
3
1407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

Hi Ben,

 

You need to first make sure of what version of SNMP is being used on the NMS (Version 1 / Version 3) and it must match what is set on the NB200.

You should only have 1 of the 2 versions enabled at at time. I have seen strange things occur if you enable both version 1 and version 3 on the APC NMC based devices such as the 200.

You need to match the community names being used in the NMS with those being used on the NB200.

If the NB200 community names have an associated IP, try setting it to all 0s for testing:

If there is an associated IP, then only that IP can use that community name. If it is set to all 0s, any host can poll the device.

 

Since you're getting an unauthorized access error, if it originates from the IP of the NMS in question, we can be pretty sure it is based on Community strings / passphrases,  associated IPs, the protocol being enabled correctly. There is more to troubleshooting SNMP we know the network is not blocking the traffic (again assuming the error is from the IP of the NMS).

Steve

(CID:105456891)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

0 Likes
3
1408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

Hi Ben,

 

You need to first make sure of what version of SNMP is being used on the NMS (Version 1 / Version 3) and it must match what is set on the NB200.

You should only have 1 of the 2 versions enabled at at time. I have seen strange things occur if you enable both version 1 and version 3 on the APC NMC based devices such as the 200.

You need to match the community names being used in the NMS with those being used on the NB200.

If the NB200 community names have an associated IP, try setting it to all 0s for testing:

If there is an associated IP, then only that IP can use that community name. If it is set to all 0s, any host can poll the device.

 

Since you're getting an unauthorized access error, if it originates from the IP of the NMS in question, we can be pretty sure it is based on Community strings / passphrases,  associated IPs, the protocol being enabled correctly. There is more to troubleshooting SNMP we know the network is not blocking the traffic (again assuming the error is from the IP of the NMS).

Steve

(CID:105456891)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

In response to DCIM_Support
0 Likes
0
1407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

P.S. K-base FA226273 may be halpful for troubleshooting SNMP issues: http://www.apc.com/site/support/index.cfm/faq/ Steve

(CID:105456893)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

In response to DCIM_Support
0 Likes
0
1407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

Thanks there was more than one IP associated with the community name and it wasn't being allowed due to it being the 2nd of the 2.

Changing it to 0.0.0.0 worked as you suggested.

(CID:105457139)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

In response to DCIM_Support
0 Likes
0
1407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2024-04-09 02:02 AM

Glad we could figure it out. Steve

(CID:105457140)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2023-10-31 11:23 PM

0 Likes
0
1407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:14 PM . Last Modified: ‎2023-10-31 11:23 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore