Netbotz 200 Connection to Cisco 2248TP

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz 200 Connection to Cisco 2248TP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
128
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:41 PM . Last Modified: ‎2024-04-09 04:08 AM

0 Likes
4
629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:41 PM . Last Modified: ‎2024-04-09 04:08 AM

Netbotz 200 Connection to Cisco 2248TP

Hello All,

Has anyone seen any issues connecting the Netbotz 200 with a Cisco 2248tp?

We have several Netbotz 200 and are struggling to get a consistent connection to a variety of Cisco 2248TP Fabric Extenders.

Some will connect straight away, some will only  sync up when we force 100 Full-duplex, some will become 100 Half-Duplex and various other combinations.

 

Symptom is that the link light on the 2248TP does not come on and  the NB200 (via Serial console) says Link Down).  Plugging in to a different device the link light on the FEX works, taking the NB200 to another FEX may or may not work.  Taking a working NB200 and plugging a different NB200 (same FW) wont work.

Very confused.

The FW on the Nb200 are all the same at ...

NB200: v3.7.5

AOS: v3.7.5

Thanks

Craig

(CID:99157968)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:41 PM . Last Modified: ‎2024-04-09 04:07 AM

0 Likes
0
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:41 PM . Last Modified: ‎2024-04-09 04:07 AM

Yes - I have had issues with a NB 450 and Symmetra ups connecting to FEX modules. Checked/tried everything. Thinking nexus bug. Ended up connecting to a catalyst with no issues.

 

(CID:99158147)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:41 PM . Last Modified: ‎2024-04-09 04:07 AM

0 Likes
0
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:41 PM . Last Modified: ‎2024-04-09 04:07 AM

I believe this is a known issue between NMC1 products and Nexus switches, where the NMC will continually fail to negotiate to 100/F no matter what switch port or NMC setting is used. We see this issue on literally hundreds of devices, and have had to resort to placing NMC1 devices on 48-port unmanaged switch/hubs that can deal with 10/H and 100/H just to get comms consistency.

(CID:99157995)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:41 PM . Last Modified: ‎2024-04-09 04:07 AM

0 Likes
0
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:41 PM . Last Modified: ‎2024-04-09 04:07 AM

Dear Craig Oberg

                  Verify Following steps.

  1. Please Disconnect the Device NB200 from the Cisco 2248TP and now Connect the NB200 via Ethernet cable [Straight Configuration] to your PC.
  2.  Check the Speed of your Device just like the snapshot below 
  3. as the Snapshot brief that your connect speed is 1.0 Gbps .
  4. same while now connect your PC with the Port on the Cisco 2248TP and check the same that whether it is same as your device or it is varied...
  5. But Note that you have not to assign your device or PC a static IP .... it will have to find automatically. as screen shot.
  6. Now if the speed is Varied from each other then connect the networking team they will set your port speed and you also have to set your Netbotz 200 to following snapshot setting.
     

 

 

 

(CID:101613711)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:41 PM . Last Modified: ‎2023-10-31 11:23 PM

0 Likes
0
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:41 PM . Last Modified: ‎2023-10-31 11:23 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore