NetBotz NFS External Storage Mount

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz NFS External Storage Mount
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:11 AM

0 Likes
9
2109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:11 AM

NetBotz NFS External Storage Mount

Dear Team,

I have a customer who needs the NetBotz 570 data stored externally to the WD My Cloud network drive via NFS.

I have tried to mount the NFS share to the NetBotz but no success, kindly anyone with any suggestions I shall gladly appreciate.

 

Thank you.

Regards,

Felix.

 

 

(CID:109447496)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:11 AM

0 Likes
7
2109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:11 AM

Hi Felix,

 

You may have noticed there is no user access information on the NFS mount option in AV. You must instead create rights on the NFS share for the NetBotz appliance by IP. I'm not familiar with "My Cloud" so I am not sure what options it may have for configuration. Maybe someone else in the forum has experience with it.  You may also want to check the NetBotz appliance logs to see if it has noted anything specific about the failure to mount.

 

Steve

(CID:109447527)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:11 AM

0 Likes
7
2110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:11 AM

Hi Felix,

 

You may have noticed there is no user access information on the NFS mount option in AV. You must instead create rights on the NFS share for the NetBotz appliance by IP. I'm not familiar with "My Cloud" so I am not sure what options it may have for configuration. Maybe someone else in the forum has experience with it.  You may also want to check the NetBotz appliance logs to see if it has noted anything specific about the failure to mount.

 

Steve

(CID:109447527)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:11 AM

In response to DCIM_Support
0 Likes
0
2109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:11 AM

Hi Steven, Thank you for your response, please find attached appliance logs for your perusal. Regards, Felix.

4.jpg

(CID:109447588)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:11 AM

In response to DCIM_Support
0 Likes
0
2109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:11 AM

Nope...nothing there. Maybe capture the serial output on boot of the bot. Did you verify that the IP of the bot has full read, write, create access on your NFS? Steve

(CID:109447595)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:10 AM

In response to DCIM_Support
0 Likes
0
2109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:10 AM

Please find attached on the settings both on the bot and NFS share. Thank you. Felix

5.jpg

6.jpg

7.jpg

(CID:109447597)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:10 AM

In response to DCIM_Support
0 Likes
0
2109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:10 AM

Felix, when you configure this setting, the appliance reboots. Please connect a USB cable from the appliance to a computer and run hyperterminal or putty and open a serial connection. Print the output of that to a file. Set up the NFS info on the appliance and allow the reboot and capture that data. Steve

(CID:109447661)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:10 AM

In response to DCIM_Support
0 Likes
0
2109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:27 AM . Last Modified: ‎2024-04-08 04:10 AM

Hi Steve, Well noted, find attached. Thank you. Felix

netbotnfs.TXT

(CID:109447681)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:28 AM . Last Modified: ‎2024-04-08 04:10 AM

In response to DCIM_Support
0 Likes
0
2109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:28 AM . Last Modified: ‎2024-04-08 04:10 AM

Felix, It looks like permissions and I can't tell you how to change that on your "My Cloud" box: This is from the logs you sent Starting portmap daemon: portmap. mount: 192.168.0.11:/netbotz failed, reason given by server: Permission denied mount: nfsmount failed: Bad file descriptor mount: Mounting 192.168.0.11:/netbotz on /opt/netbotz/mnt failed: Bad file descriptor root: Waiting to retry mount of 192.168.0.11:/netbotz using nfs... root: Attempting mount of 192.168.0.11:/netbotz using nfs... mount: 192.168.0.11:/netbotz failed, reason given by server: Permission denied Steve

(CID:110004038)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:28 AM . Last Modified: ‎2024-04-08 04:10 AM

In response to DCIM_Support
0 Likes
0
2109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:28 AM . Last Modified: ‎2024-04-08 04:10 AM

Hi Steve, I will try to check again on the permissions. Thank you. Felix

(CID:110004150)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 07:28 AM . Last Modified: ‎2023-10-22 03:13 AM

0 Likes
0
2109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 07:28 AM . Last Modified: ‎2023-10-22 03:13 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore