New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
NetBotz 755 Error after Firmware Update
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-0406:10 AM
NetBotz 755 Error after Firmware Update
Hi All,
I have just updated the Firmware on my NetBotz 755 from v5.2.1 to v5.3.5 and I am now getting an Alarm on DCE v7.9.0 that says "Device Status may be inaccurate because an attempt to transfer a device definition file (DDF) failed."
The NetBotz are located at Remote Sites and I performed the upgrades via the web client.
This alarm was not there prior to the firmware update.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-10-0506:37 AM
Hello,
try to verify on DCE > device > netbotz appliance communication settings > netbotz appliance credentials (you must have web user)
also on device > snmp device communication settings > device file transfer settings > netbotz ip with protocol SCP and use root (you can try on ssh if you can login with root...also is possible to not have a root password and you must set it )
or update to DCE 8.0.0 which does not require SCP connection and DDF can be retrieved via http/s