NetBotz 550 Motion Detected but no Picture Attachment

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz 550 Motion Detected but no Picture Attachment
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:28 PM . Last Modified: ‎2024-04-09 04:31 AM

0 Likes
8
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:28 PM . Last Modified: ‎2024-04-09 04:31 AM

NetBotz 550 Motion Detected but no Picture Attachment

Hi Team,

I had configured Pelco Sarix Camera to NetBotz 550 and motion used to be detected and images sent as attachement via email.

The client reported that the motion detected email alert is being recieved but no pictures attached.

I have checked all the configuration and they seem to be ok, I tried to remove and rediscover the cameras but still no picture attachment.

Please see below screen shots of my configuration and advise. Could there be a network change that has triggered this? who has experienced this before and how can I solve it?

Regards,

Felix

(CID:97486143)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:28 PM . Last Modified: ‎2024-04-09 04:31 AM

0 Likes
2
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:28 PM . Last Modified: ‎2024-04-09 04:31 AM

Hi Felix,

 

Are you seeing images in the alert? You show 236 alerts for the last 3 years, do they all include images when viewed through advanced view (AV)?

What Pelco camera are you using?

What version of Botzware and Advanced View are you using?

To how many e-mail addresses are you sending this alert?

Can you test sending with lower resolution and less frame rate? 

What alert action are you using? (send e-mail, primary e-mail, sms?)

In the alert action what is the picture export format?

Is the target e-mail one in the alert action or a threshold specific addres

In the alert profile and the specific sequence you are using for this alert action, What are the capture settings for the pictures option?

 

Can you test this specific motion threshold with a new profile. Create a new alert action with a single e-mail address. Maybe even a different address to be sure the e-mail server is not stripping out the images. Use a small image and low frame rate. Make sure the sequence is always set to capture pictures. Create motion and verify it is seen. Verify the alert in AV includes these images. Check e-mail.

 

If the e-mail does not include the images, go to the bot using a web browser. Go to:

http://172.16.8.14/pages/support.html

Click the logread button. Attach the portion of the log that pertains to the timeperiod in question. We'll see if the bot is seeing anything.

 

Steve

 

 

 

(CID:97486158)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:28 PM . Last Modified: ‎2024-04-09 04:31 AM

In response to DCIM_Support
0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:28 PM . Last Modified: ‎2024-04-09 04:31 AM

Are you seeing images in the alert? YES You show 236 alerts for the last 3 years, do they all include images when viewed through advanced view (AV)? ALERTS SHOWING ATTACHMENT STOP AT DATE 19/06/15 What Pelco camera are you using? PELCO SARIX IM10C10 What version of Botzware and Advanced View are you using? V 4.3.0 To how many e-mail addresses are you sending this alert? 3 EMAIL ADDRESS Can you test sending with lower resolution and less frame rate? TRIED What alert action are you using? (send e-mail, primary e-mail, sms?) PRIMARY E-MAIL In the alert action what is the picture export format? JPEG Is the target e-mail one in the alert action or a threshold specific addres ALERT ACTION In the alert profile and the specific sequence you are using for this alert action, What are the capture settings for the pictures option? ALWAYS CAPTURE

(CID:97486167)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:28 PM . Last Modified: ‎2024-04-09 04:31 AM

In response to DCIM_Support
0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:28 PM . Last Modified: ‎2024-04-09 04:31 AM

Hi Steve, Please see below few lines of the logread that relate to the camera motion Jun 23 15:43:36 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: Camera capture started: camera=nbRmtEnclosure_2_nbCamera_0 Jun 23 15:43:36 DR_DataCentre_NetBotz daemon.err nbAlertMgr: nbAlertCaptureActionStart: still running 'nbCameraCapture/nbRmtEnclosure_2_nbCamera_0/nbErrorCond_45371BEE' Jun 23 15:43:36 DR_DataCentre_NetBotz daemon.err nbCaptureMgr: nbFileSetAddDataChain: error opening /opt/netbotz/mnt/DRCCTV/NetBotz_DR_Backup/00_C0_B7_9C_C2_F6/16609/12/26160000/campic0000.jpg (errno=13) Jun 23 15:43:36 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: Picture 1 of 10 failed Jun 23 15:43:38 DR_DataCentre_NetBotz daemon.err nbCaptureMgr: nbFileSetAddDataChain: error opening /opt/netbotz/mnt/DRCCTV/NetBotz_DR_Backup/00_C0_B7_9C_C2_F6/16609/12/26160000/campic0000.jpg (errno=13) Jun 23 15:43:38 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: Picture 2 of 10 failed Jun 23 15:43:39 DR_DataCentre_NetBotz daemon.err nbCaptureMgr: nbFileSetAddDataChain: error opening /opt/netbotz/mnt/DRCCTV/NetBotz_DR_Backup/00_C0_B7_9C_C2_F6/16609/12/26160000/campic0000.jpg (errno=13) Jun 23 15:43:39 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: Picture 3 of 10 failed Jun 23 15:43:40 DR_DataCentre_NetBotz daemon.err nbCaptureMgr: nbFileSetAddDataChain: error opening /opt/netbotz/mnt/DRCCTV/NetBotz_DR_Backup/00_C0_B7_9C_C2_F6/16609/12/26160000/campic0000.jpg (errno=13) Jun 23 15:43:40 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: Picture 4 of 10 failed Jun 23 15:43:41 DR_DataCentre_NetBotz daemon.err nbCaptureMgr: nbFileSetAddDataChain: error opening /opt/netbotz/mnt/DRCCTV/NetBotz_DR_Backup/00_C0_B7_9C_C2_F6/16609/12/26160000/campic0000.jpg (errno=13) Jun 23 15:43:41 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: Picture 5 of 10 failed Jun 23 15:43:42 DR_DataCentre_NetBotz daemon.err nbCaptureMgr: nbFileSetAddDataChain: error opening /opt/netbotz/mnt/DRCCTV/NetBotz_DR_Backup/00_C0_B7_9C_C2_F6/16609/12/26160000/campic0000.jpg (errno=13) Jun 23 15:43:42 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: Picture 6 of 10 failed Jun 23 15:43:43 DR_DataCentre_NetBotz daemon.err nbCaptureMgr: nbFileSetAddDataChain: error opening /opt/netbotz/mnt/DRCCTV/NetBotz_DR_Backup/00_C0_B7_9C_C2_F6/16609/12/26160000/campic0000.jpg (errno=13) Jun 23 15:43:43 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: Picture 7 of 10 failed Jun 23 15:43:44 DR_DataCentre_NetBotz daemon.err nbCaptureMgr: nbFileSetAddDataChain: error opening /opt/netbotz/mnt/DRCCTV/NetBotz_DR_Backup/00_C0_B7_9C_C2_F6/16609/12/26160000/campic0000.jpg (errno=13) Jun 23 15:43:44 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: Picture 8 of 10 failed Jun 23 15:43:45 DR_DataCentre_NetBotz daemon.err nbCaptureMgr: nbFileSetAddDataChain: error opening /opt/netbotz/mnt/DRCCTV/NetBotz_DR_Backup/00_C0_B7_9C_C2_F6/16609/12/26160000/campic0000.jpg (errno=13) Jun 23 15:43:45 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: Picture 9 of 10 failed Jun 23 15:43:47 DR_DataCentre_NetBotz daemon.err nbCaptureMgr: nbFileSetAddDataChain: error opening /opt/netbotz/mnt/DRCCTV/NetBotz_DR_Backup/00_C0_B7_9C_C2_F6/16609/12/26160000/campic0000.jpg (errno=13) Jun 23 15:43:47 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: Picture 10 of 10 failed Jun 23 15:43:47 DR_DataCentre_NetBotz daemon.notice nbCameraMgr: capture_request_complete: Capture completed (camid=nbRmtEnclosure_2_nbCamera_0, filesetid=nbFileSet_16609_12_26160000) Jun 23 15:43:47 DR_DataCentre_NetBotz daemon.notice nbAlertMgr: Camera capture complete - fileset=nbFileSet_16609_12_26160000 Jun 23 15:43:47 DR_DataCentre_NetBotz daemon.notice nbSendEmailAlert: Send E-mail Alert started Regards, Felix

(CID:97486170)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:29 PM . Last Modified: ‎2024-04-09 04:31 AM

0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:29 PM . Last Modified: ‎2024-04-09 04:31 AM

Hi Felix,

 

Are you also using DCE? If so, what version? The only issue I've seen even close to this was related to an older DCE.

I noticed you have 2 cameras, both appear to be Pelco (hot isle and cold isle). Are they both doing the same thing?

I also noticed that since you have 3 year old alerts, you must be using remote storage. Is it possible, for a test, to put the remote share off-line so we can make sure the bot is only looking locally to get the images rather than potentially remotely? Don't tell the bot to stop using so that a reboot of the bot will reconnect assuming the share is back on-line.

 

Before the next test, please go to the log applet in AV. Set the global level to critical. Set any camera or capture specific component to trace. If using surveillance, set that to trace as well. Please set the UPnP component to trace as well. Run another test and then set these components back to global level and the global level back to where it was prior to this test.

 

Steve

 

(CID:97486177)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:29 PM . Last Modified: ‎2024-04-09 04:31 AM

0 Likes
2
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:29 PM . Last Modified: ‎2024-04-09 04:31 AM

Hi Steve,

I have stopped the external storage backup and the email alerts are being recieved with attached images. I am not sure why that is so, but I am still investigating.

Regards,

Felix

(CID:97486179)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:29 PM . Last Modified: ‎2024-04-09 04:31 AM

In response to DCIM_Support
0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:29 PM . Last Modified: ‎2024-04-09 04:31 AM

Felix, I believe the images are stored remotely then the bot needs to pull them back to send in the e-mail. There could either be a network latency or there could be a rights issue on the drive. Is the drive local? Have you tried attaching a NetBotz camera to this same appliance for testing to see if those images can be retrieved? Steve

(CID:97486188)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:29 PM . Last Modified: ‎2024-04-09 04:31 AM

In response to DCIM_Support
0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:29 PM . Last Modified: ‎2024-04-09 04:31 AM

Steve, The Customer has two sites, one the Main DC and the other the DR. In both DC I had configured the NetBotz appliances External backup storage to the same windows share in a Server at the Main DC. The two NetBotz appliances stopped sending images at the same time despite being in two different geographical location. I therefore dismounted the windows share and now they work perfectly, the problem has to be with the windows share. Thanks a lot Steve, much appreciated. Regards, Felix

(CID:97486193)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:29 PM . Last Modified: ‎2023-10-31 11:25 PM

0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:29 PM . Last Modified: ‎2023-10-31 11:25 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore