NetBotz 4.x: how to remove non-existent sensors from AV, with N/A readings?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz 4.x: how to remove non-existent sensors from AV, with N/A readings?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:58 AM . Last Modified: ‎2024-04-05 03:39 AM

0 Likes
3
1401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:58 AM . Last Modified: ‎2024-04-05 03:39 AM

NetBotz 4.x: how to remove non-existent sensors from AV, with N/A readings?

Hi all!

On the above mentioned problem, unfortunately, I was able to find here on EcoStruxure IT only one solution -- it is resetting the NetBotz appliance to the factory default settings. For example, an instruction on how to do this was published in topic .

Problem essence: in sensor ports 1 and 2 of NetBotz-450 appliance with 4.6.1 firmware were connected of the temperature and humidity sensors AP9335TH. Then these two sensors were physically disconnected and the NetBotz appliance was turned off. Then, dry contacts NBES0304 were connected to the sensor ports 1, 2 and 3 and the NetBotz appliance was turned on.

But in the AV interface, the temperature and humidity sensors have remained. Of course their readings are displayed as N/A and for some reason they can not be removed:

We tried to disconnect all dry contacts from the sensor ports 1, 2 and 3. But above the Remove button for temperature and humidity sensors was also not active (but was active for disconnected dry contacts). Updating the NetBotz appliance to the current version 4.6.2 and restarting it did not solve the problem.

Is the only solution to this problem is to reset NetBotz appliance to the factory default settings?

Very thanks for the support.

(CID:126882460)

Labels
  • Labels:
  • NetBotz
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:58 AM . Last Modified: ‎2024-04-05 03:39 AM

0 Likes
0
1401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:58 AM . Last Modified: ‎2024-04-05 03:39 AM

Hi all!

Thanks to Steven Marchetti answer in post , I remotely was able to successfully solve the above mentioned problem with the NetBotz-450 appliance. I.e., I was able to remotely reset the device to the factory default settings (of course except for the basic IP settings) and even without reconnecting all external sensors.

To do this, as indicated in the above post, I entered the browser at address http://your_netbotz_address/unconfig. Confirmations of the reset to the factory default command are not needed, and within a few minutes the device rebooted and switched back to online mode with initial settings and all normal connected external sensors without of non-existent sensors in the AV with N/A readings. After that, I also remotely could normally perform all necessary configurations of the NetBotz-450 and rediscover it in the DCE-server. Great result 😀.

I hope this will be useful for many people remotely working with NetBotz-4.x appliances.

With respect.

(CID:128758790)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:58 AM . Last Modified: ‎2024-04-05 03:39 AM

0 Likes
0
1401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:58 AM . Last Modified: ‎2024-04-05 03:39 AM

Hi spezialist, thanks for sharing. Let's hope you find your answer here 😀Kind regards Ditte

(CID:126886122)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:58 AM . Last Modified: ‎2024-04-05 03:39 AM

0 Likes
0
1402
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:58 AM . Last Modified: ‎2024-04-05 03:39 AM

Hi all!

Thanks to Steven Marchetti answer in post , I remotely was able to successfully solve the above mentioned problem with the NetBotz-450 appliance. I.e., I was able to remotely reset the device to the factory default settings (of course except for the basic IP settings) and even without reconnecting all external sensors.

To do this, as indicated in the above post, I entered the browser at address http://your_netbotz_address/unconfig. Confirmations of the reset to the factory default command are not needed, and within a few minutes the device rebooted and switched back to online mode with initial settings and all normal connected external sensors without of non-existent sensors in the AV with N/A readings. After that, I also remotely could normally perform all necessary configurations of the NetBotz-450 and rediscover it in the DCE-server. Great result 😀.

I hope this will be useful for many people remotely working with NetBotz-4.x appliances.

With respect.

(CID:128758790)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:58 AM . Last Modified: ‎2023-10-22 03:12 AM

0 Likes
0
1401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:58 AM . Last Modified: ‎2023-10-22 03:12 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore