Having issues with a newly configured Netbotz 355. I set the unit up and everything seemed good. I went home and started getting alerts about the integrated sensor pod getting unplugged. After getting back
The device is still on the network and reachable, the camera still works and I can config it in Advanced View. If I go to the web page and login, and go to alerts it shows "Sensor Pod - unplugged" and under Pods it shows the integrated pod is disconnected. It does not sure values from the internal sensors or any sensors that I connect (AP9335TH or NBES0302). Before it stopped working, I did connect 2 AP9335TH to it and is registered those sensors and still shows them in the web page but show N/A for all of them.
Is there any factory restore procedure or anything else I can try to get this thing functional again ?
Thanks !!!
(CID:105471565)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:06 AM . Last Modified: 2024-04-09 12:23 AM
Hi Jason,
I would first suggest disconnecting all sensors then resetting the unit
To reset the device to defaults, connect a USB cable to the unit and launch putty or hyperterminal to it. Reboot the device and you should see it starting up in putty. When it says to stop the boot, hit any key and starts counting down, hit a key. When at a command prompt type in all one word:
configreset
The bot should then reboot again and reset itself to defaults. If the issue remains or reappears, I would suggest contacting tech support directly to see about a replacement unit. If the issue only appears when connecting the sensors back ( make sure they're in the right connectors) it could also have something to do with the sensors.
Steve.
(CID:105471568)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:06 AM . Last Modified: 2024-04-09 12:23 AM
Hi Jason,
I would first suggest disconnecting all sensors then resetting the unit
To reset the device to defaults, connect a USB cable to the unit and launch putty or hyperterminal to it. Reboot the device and you should see it starting up in putty. When it says to stop the boot, hit any key and starts counting down, hit a key. When at a command prompt type in all one word:
configreset
The bot should then reboot again and reset itself to defaults. If the issue remains or reappears, I would suggest contacting tech support directly to see about a replacement unit. If the issue only appears when connecting the sensors back ( make sure they're in the right connectors) it could also have something to do with the sensors.
Steve.
(CID:105471568)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:06 AM . Last Modified: 2024-04-09 12:23 AM
Steve thanks for the info, I have now reset to factory. Unfortunately this did not solve my problem... now the integrated sensor pod isn't seen anywhere, nor is there any reference to it. I called support and they are sending out a replacement unit since the unit was brand new.
Thanks for the steps on the serial connection to the unit, I didn't realize that USB port was for serial, I thought maybe it was just for connecting external pods or cameras.
Anyone else who might find this make sure you find your COMM port number that the USB port is on and then change the baud rate on your connect to 38400 and you will be in.
Thanks
Jmac
(CID:105471993)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:06 AM . Last Modified: 2023-10-31 11:23 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.