NB spot fluid sensors (NBES0301) detecting fluid when none present

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NB spot fluid sensors (NBES0301) detecting fluid when none present
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:32 PM . Last Modified: ‎2024-04-08 12:36 AM

0 Likes
9
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:32 PM . Last Modified: ‎2024-04-08 12:36 AM

NB spot fluid sensors (NBES0301) detecting fluid when none present

Hi Everyone

Wanted to see if someone could kindly assist with my issue?

We have recently purchased and installed 2 Netbotz 250 each with 3 NetBotz 150 spot fluid sensors attached. They are located in two different server rooms.

3 of the sensors connected to one of the monitors and 1 sensor connected to the other monitor are continually setting off critical warnings for detected fluid when there is no fluid present. 

I would say however, the alerts are going off out of hours, sometimes 10 at night, 3 in the morning, 6 in morning etc. but upon inspection of both server rooms, there is clearly no fluid on the floor or around the sensors when checked.

A little installation background info....

Both Netbotz 250's have had firmware updated. All are placed on plastic insulation sheets (more as a test than any other reason, as the floor is vinyl). Room humidity is low (around 25-30%). Some sensors are extended using couplers, some are not. Rooms are pretty air tight. Have tried moving sensors to different ports.

My questions are:

  1. Are these sensors super sensitive?
  2. Can you configure them? In the documentation it states for the configuration:
    "Once the Spot Fluid Sensor is conected to the NetBotz Appliance, it will be detected automatically, and will appear in the Sensor Readings pane. The Spot Fluid Sensor is a normally open (NO) dry contact sensor. Use the Dry Contact task to configure the settings for the NetBotz Spot Fluid Sensor. See the NetBotz Appliance User’s Guide for more information about the Advanced View."
    But I can not see how to do this within the admin console for the NetBotz
  3. Could they just be faulty and we are unlucky to have received 4 out of an order of 6?

Any help or advice would be gladly received.

Thanks

Chris

 

 

(CID:119638090)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:32 PM . Last Modified: ‎2024-04-08 12:36 AM

0 Likes
4
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:32 PM . Last Modified: ‎2024-04-08 12:36 AM

Hi Chris,

 

There is no sensitivity configuration to the sensors. The only thing you can configure in NetBotz Advanced View (only to use with the 3xx, 4xx, and 5xx series units) is the alert configuration. I'll also have to look at that document you mention as I believe it may be worded incorrectly.

The only thing they do is monitor conductivity between the 4 contacts. It is a little suspect also that they only alert when there's nobody to check them. Are you sure there is no condensation?

Is it always the same sensors? If you have one unit that has a single sensor tripping and 2 others that do not, try swapping port and position. Put the working sensor where one seems to be failing and let it go for a time. Does the issue follow the sensor or the placement / port?

 

Thanks,

Steve.

(CID:119638116)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:32 PM . Last Modified: ‎2024-04-08 12:35 AM

In response to DCIM_Support
0 Likes
0
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:32 PM . Last Modified: ‎2024-04-08 12:35 AM

Hi Steve

Thanks for your response ... was just typing a response and the site went down!

Pretty sure its not a condensation thing ... with a very low humidity reading on sensors, I kind of ruled that out.

As you suggested I will try swapping the 2 sensors that haven't triggered so far with the ones that have and will see what happens.

The other thing that just occurred to me, is that the 3 of the faulty sensors are connected to monitor using structured cabling (but within the length limit), so wondered if this might be a factore. But, just to confuse things further, the other faulty sensor in our other server room is not connected via structured cabling.

I'll re-post if I have any success.

Thanks again

Chris 

(CID:120129566)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:32 PM . Last Modified: ‎2024-04-08 12:35 AM

In response to DCIM_Support
0 Likes
0
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:32 PM . Last Modified: ‎2024-04-08 12:35 AM

Just an update for anyone following this thread ....

I contacted APC support and got a useful response back that hopefully should resolve this issue.

So for reference, the NetBotz RM appliances only support up to 2 spot fluid detectors, so this is probably why ours were giving inaccurate warnings. If you want more, you need to purchase a Pod Sensor 150, for which you can add an additional 2 spot fluid sensors to.

I have unplugged the 3rd sensor on each of our monitors and will wait and see.

Thanks for viewing and to Steven for advice!

(CID:120131260)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2024-04-08 12:35 AM

In response to DCIM_Support
0 Likes
0
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2024-04-08 12:35 AM

Actually, the 3xx, 4xx, and 5xx have a built in limitation of 2 spot leak sensors per pod. The 250 (which you said you were using) has no such limitation. If you ran into that limitation, you would simply not see the sensor.

(CID:120131258)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2024-04-08 12:35 AM

In response to DCIM_Support
0 Likes
0
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2024-04-08 12:35 AM

Thanks Steven ... I shall go back to them with that and also, even with unplugging one of the sensors, it has still just gone off randomly.

Guess this is not resolved just yet!

(CID:120131254)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2024-04-08 12:35 AM

0 Likes
2
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2024-04-08 12:35 AM

Latest info from APC support ....

The device  does support more than 2 spot fluid detectors for sure but the issue I have has been confirmed as a Firmware issue and will 'hopefull' be resolved when they release the next revision.

Not too impressed with that to be honest but that is where I am with this issue.

(CID:120132960)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2024-04-08 12:35 AM

In response to DCIM_Support
0 Likes
0
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2024-04-08 12:35 AM

Hi Chris,

 

What testing leads you to the belief that it is a firmware issue?

What firmware are you running on the 250s?

It's my understanding that we've done testing with devices / pods full of these and not see the issue that you're seeing. Have you taken the devices and sensors out of the environment  to make sure there's no signal being induced on the lines or other strange occurrences? I don't mean to prolong this issue for you but if our engineers don't replicate it, there's no way it will be fixed if it is indeed a firmware issue.


Steve

(CID:120133028)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2024-04-08 12:35 AM

In response to DCIM_Support
0 Likes
0
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2024-04-08 12:35 AM

Hi Steve

We are running latest firmware 6.4.6.

No, I haven't taken them out of the environment they were set up in to test. The only testing I have done, is to plug them directly into sensor ports on the 250 (they were using some structured cabling to route them to the 250 - only one of the monitors though). Remove the cable ties that were securing the cables and removing the 3rd sensor, leaving just 2 per monitor and re-locate them to another area of the computer rooms - away from air-con units.

The support case I logged with your colleagues (Ref: 00DA0abSm) was how I received this information about it being a known error.

Here is the direct response:

"Me seniors have replied back and they confirm that this appears to be a bug in the current firmware v6.4.6.  Hence the reason why you are getting the 'random' false trigger from the spot fluid sensors.  The Product Development Teams are aware of this issue and the bug will be addressed in a future firmware release.  At this time, we can not forecast when the new firmware will be available.  I shall keep the case open for you and when the firmware is released, I shall provide this to you.  However you can also monitor on the product page for new firmware releases: http://www.apc.com/shop/ie/en/categories/security-and-environmental-monitoring/security-and-environm...

Lastly, I would like to confirm that the Netbotz 250 does 'not' have limitation to the number of spot fluid sensors."

Thanks

Chris

(CID:120133057)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2023-10-22 03:06 AM

0 Likes
0
1658
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:33 PM . Last Modified: ‎2023-10-22 03:06 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore