MTCBA-G2-U stops sending SMS alerts on NBRK0550

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • MTCBA-G2-U stops sending SMS alerts on NBRK0550
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:34 PM . Last Modified: ‎2024-04-09 03:07 AM

0 Likes
11
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:34 PM . Last Modified: ‎2024-04-09 03:07 AM

MTCBA-G2-U stops sending SMS alerts on NBRK0550

Dear Team,

I have noticed the MTCBA-G2-U multitech modem stops sending SMS after some days and I have to reboot the NetBotz 550 appliance in order for it to resume sending SMS on to stop again.

Kindly is this a firmware issue on the NetBotz appliance? has anyone experienced this?

Regards,

Felix

(CID:102924801)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:34 PM . Last Modified: ‎2024-04-09 03:07 AM

0 Likes
8
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:34 PM . Last Modified: ‎2024-04-09 03:07 AM

Hi Felix,

 

There is no known firmware issue that would cause this. It is likely a process within the appliance that is getting hung up. This could be due to the modem itself or it could be related to other components or configurations.

 

How often does this occur? Is it happening every time the modem is used? Is it happening every day? Every week? Month? What firmware are you running on the appliance? The most recent is 4.5.

 

Are you able to access the appliance immediately after the issue occurs? If so, note the time the issue occurred as well as obtaining the logs from the device. They are most easily saved from the web page of the device at:

http:///cgi-bin/nbSupportCGI?cmdid=logread

 

If it is happening very frequently, you may also want to back up th appliance and do some testing. reset the bot to defaults and configure only the modem and a single threshold, wet it off a few times to see if the issue repeats itself. There may be a configuration (physical or software) that is causing the appliance to have issues and this should resolve any software issues. If this resolves the issue, you may want to consider a manual reconfiguration as re-importing a backup could re-import the issue.

 

Steve

(CID:102924851)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:34 PM . Last Modified: ‎2024-04-09 03:06 AM

In response to DCIM_Support
0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:34 PM . Last Modified: ‎2024-04-09 03:06 AM

Hi Steven, The modem takes two days at most and SMS stops sending. I have tried firmware reset and re-entered the configuration manually but after two days the modem stopped sending alerts. This problem is similar to another site in a different geographical region. The customer is really unhappy with this and I am considering changing the modem to another one hoping it clears this issue. I am visiting site and will send you the logs once I have them. Regards, Felix

(CID:102925201)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

In response to DCIM_Support
0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

Hi Steven,

 

Please find attached screen shot presumably showing when the modem stops sending alerts.

What results to locking of the serial port?

 

Also find the below screen shot of the other site which is experiencing the same problem.

 

Regards,

Felix

 

(CID:102925269)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

In response to DCIM_Support
0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

Hi Steve, The NetBotz firmware is rev 4.3 as this supports MTCBA-G2-U, I cannot upgrade to 4.5 because I shall need to change the Modem. Regards, Felix

(CID:102925298)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

In response to DCIM_Support
0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

Does firmware version 4.5 do not support MTCBA-G2-U modem?

(CID:102925313)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

In response to DCIM_Support
0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

Hi Balaraman, I have not tested it with rev4.5 but it does not work with 4.4 and it was mentioned that it best works with rev4.3 or below. Regards, Felix

(CID:102925316)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

In response to DCIM_Support
0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

Felix, Please upgrade to 4.5. There were known issues with 4.4 and modems. You can always back the unit up and if necessary, go back to 4.3.

(CID:102925344)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

In response to DCIM_Support
0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

Hi Steve, Thank you for your response. I shall do that and advise hoping that this will solve the locking of the serial port connecting the modem. Regards, Felix.

(CID:102925387)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

In response to DCIM_Support
0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

Welcome. I know it resolves the 4.3 to 4.4 issue you've seen. Can't say 100% it resolves the other. If possible, Can you download the logs in text format via the link I provided should it continue to fail? Steve

(CID:102925414)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2024-04-09 03:06 AM

Hi Felix, I have done the modem(MTCBA-G2-U) insatallation with 4.5 firmware in 4 nos netbotz and its working fine from last 1 month.

(CID:103584079)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2023-10-31 11:22 PM

0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:35 PM . Last Modified: ‎2023-10-31 11:22 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore