Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Lost Communcation Alert

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Lost Communcation Alert
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

0 Likes
10
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

Lost Communcation Alert

I upgraded a network management card to v6.8.2, Struxureware is showing a lost comm alert for this device.  I can, however remote to it in struxureware and view the card just fine.  I've tried resetting the card and rebooting the struxureware server to no avail.

(CID:148344200)

Labels
  • Labels:
  • Data Center Expert
  • IT Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

0 Likes
7
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

Hi!

Did you check SNMP settings on NMC? Maybe you use specific community string or port that was changed to default during upgrade?

 

(CID:148344278)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

SNMPv1 had gotten disabled at some point in the firmware upgrade, turning that back on resolved the issue. 

(CID:148767342)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

Hi Todd,

Can you tell us what version of firmware was on the device prior to upgrading and what device as Bala had asked? We'd like to try to reproduce if possible.

 

Steve

(CID:148767816)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

Hi Todd,  do you happen to know which revision of firmware you were using prior to upgrade?

Did this happen on one device or multiple devices?  If multiple, were all devices the same type or did they vary?

The 6.8.2 upgrade contains changes pertaining to insecure protocols being disabled by default, one of which being SNMP.  However, these changes should not affect existing installations (only if you reset a device to default or you receive a new product which has shipped with version 6.8.2 or higher), so if you were doing a basic firmware upgrade, I would not expect any sort of loss of communication. 

Any additional information you can share would be greatly appreciated.

Thanks.

(CID:148767864)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

using V.6.6.4 prior.  I upgraded the card on a 1500 series ups and it didn't reset that snmp settings, just on the 5000.   I haven't tried upgrading our other 5000s yet to see if it was just a one off issue. It very well could've been due to a reset of the card.  I will install on another 5000 and test. 

(CID:148768086)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:54 PM . Last Modified: ‎2024-04-03 12:39 AM

upgraded firmware on another 5000, it did retain current settings.  looks like a one off issue.  i was troubleshooting a temperature sensor issue prior, so the card may have done a reset. 

(CID:148770476)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:55 PM . Last Modified: ‎2024-04-03 12:39 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:55 PM . Last Modified: ‎2024-04-03 12:39 AM

Hi Todd,  okay, good to hear that the 1500 one worked.  The reset on the card would be a reset to default settings, is that something you would have been trying to do?  Hope the next 5000 works okay, if it does not please let me know.  Running version 6.6.4 I wouldn't expect any issues so I would like to make sure that there is nothing possibly causing an unexpected reset which would cause SNMP to go disabled.

(CID:148768118)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:55 PM . Last Modified: ‎2024-04-03 12:39 AM

In response to DCIM_Support
0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:55 PM . Last Modified: ‎2024-04-03 12:39 AM

Hi Todd, sorry my last post overlapped your most recent one.  Glad to hear the most recent upgrade worked. 

(CID:148768122)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:55 PM . Last Modified: ‎2024-04-03 12:39 AM

0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:55 PM . Last Modified: ‎2024-04-03 12:39 AM

Dear Todd, Did you upgrade your NMC to version 6.8.2 through DCE--Updates-Apply Firmware update?

May I know the product model number in which this NMC is installed? Is it rPDU, or UPS?

Did you reset the card to factory defaults or just rebooted the NMC management interface?

In case If the card was reset to factory defaults, then please check if you are using SNMP version 1 and SNMP version 3 in DCE to communicate with the NMC.

Please check if SNMP version 1 is enabled and its community string name on NMC web interface

If disabled, DCE will show loss of communication if SNMP version 1 is used to communicate with NMC and if community string name is not matching. 

Can you share us the config.ini file of NMC? Current SNMP settings being used to communicate with DCE. 

(CID:148344336)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:55 PM . Last Modified: ‎2023-10-22 02:58 AM

0 Likes
0
1592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:55 PM . Last Modified: ‎2023-10-22 02:58 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore