Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Issues about adding NBRK0250 to NBRK0450

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Issues about adding NBRK0250 to NBRK0450
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:41 AM

0 Likes
6
1535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:41 AM

Issues about adding NBRK0250 to NBRK0450

Hi Team,

Is there anybody ever try adding  NBRK0250 to NBRK0450 (or 550/570) ?  A customer told me that he had  1*NBES0308 , 1* NBES0307  , 1*NBES0303 , 1*AP9335T and 1*AP9335TH connected to NBRK0250 , then added it to NBRK0450 . But only temperature and humidity sensor values are displayed in AV .

And I have tested with NBRK0570 , it still cannot recognize NBES0307/0803 . Pls kindly help me on this.

Both firmwares has been updated to latest version, pls seen the screenshot as bellow :


(CID:110007958)

Labels
  • Labels:
  • DDF
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:41 AM

0 Likes
3
1535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:41 AM

Dear Eric,

NBRK0250 and NBRK0450/570 are Netbotz Appliances. Please refer the Installation Manual of 450/570.

It is not possible to connect NBRK0250 to NBRK0450/570 as they are appliances. Therefore, please do not try connecting the NBRK0250 to NBRK0450/570 as its not supported. 

Regards,

Bala

(CID:110007965)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:41 AM

In response to DCIM_Support
0 Likes
0
1535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:41 AM

Hi Bala, Well, there is misunderstanding ..... Sorry for that I haven't clarified it clearly. NBRK0250 and NBRK0450 are not connected directly via any cable . i mean 250 is added into 450 as a SNMP device . Thanks Eric

(CID:110007969)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:41 AM

In response to DCIM_Support
0 Likes
0
1535
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:41 AM

Hi Eric, I am sorry for my misunderstanding. As Valentin mentioned, please check if its supported by updating the DDF file. I am not sure if the current Botzware version supports NBRK0250 to show all the readings via SNMP by having the appropriate DDF file. Secondly, I do not thing NBES0308-NetBotz Leak Rope Sensor - 20 ft. is supported by NBRK0250. As per the NBRK0250 User Manual, The following options are available for the Rack Monitor 250. NBES0308 is not listed in the supported list. NetBotz Rack Sensor Pod 150 (NBPD0150) Temperature Sensor with Digital Display (AP9520T) Temperature/Humidity Sensor with Digital Display (AP9520TH) Temperature Sensor (AP9335T) Temperature/Humidity Sensor (AP9335TH) Wireless Temperature Sensor (NBWS100T/NBWS100H) Wireless Sensor Pod 180 (NBPD0180) USB Coordinator & Router (NBWC100U) NetBotz 3.65-m (12-ft) Door Switch Sensor for APC Racks (NBES0303) NetBotz 15.24-m (50-ft) Door Switch Sensor for Rooms or Third Party Racks (NBES0302) NetBotz 125 kHz Handle Kit (NBHN0125) NetBotz 13.56 MHz Handle Kit (NBHN1356) NetBotz Dry Contact Cable (NBES0304) Alarm Beacon (AP9324) NetBotz Vibration Sensor (NBES0306) NetBotz Smoke Sensor (NBES0307) NetBotz Spot Fluid Sensor (NBES0301) Regards,Bala

(CID:110007977)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:40 AM

In response to DCIM_Support
0 Likes
0
1536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:40 AM

Hi Eric, Bala, There is no NetBotz 250 DDF on the NetBotz DDF list. It is not supported at this time. You can add it and you can use Supplemental OIDs for numeric values but DDFs are not to my knowledge being created for the NetBotz devices. Additionally, the 250 is not supported at this time when using pod sharing on the 4xx or 5xx models either. Steve.

(CID:110008031)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:40 AM

0 Likes
0
1536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2024-04-08 03:40 AM

Hi Eric!

I think you should contact your local techsupport team and create request for new DDF for netbotz. 

Or you can try to request it via Device Support page. First option will be a bit faster, I guess.

 

Also, you can try to add sensors to Netbotz using supplemental OID feature.

(CID:110007971)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2023-10-22 02:52 AM

0 Likes
0
1536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:01 AM . Last Modified: ‎2023-10-22 02:52 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore