Posted: 2025-05-20 12:47 AM
Hi guys,
Can anyone help me with some problems with DCE?
1) I have NetBotz 750 rack appliance where i planing monitor 10kW Galaxy VS UPS. I added UPS to DCE via IP but now getting err "Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed" (pic.1). Alarm type "Device Definition File (DDF) Transfer Failure ". I tried to download DDF file but didnt find it in the internet. Mybe i'm in the wrong way?
2) I have a second appliance "APC Environmental Manager (AP9340)" which is also connected to the local network and DCE. But i dont see sensors and their readings there and getting 2 errors (pic.2). Does IT DCE 8.1 support monitoring this device or not? If not, what should i do wtih this device and there is any other options to read sernsor readings?
Thx.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-22 09:39 AM
Hi @itaktau,
You can search for a DDF for these devices here: https://ddf.ecostruxureit.com
Otherwise, you'll get the best and fastest answer if you contact support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-22 09:39 AM
Hi @itaktau,
You can search for a DDF for these devices here: https://ddf.ecostruxureit.com
Otherwise, you'll get the best and fastest answer if you contact support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-22 10:11 PM
Thank you JLehr,
I already tried, donwloaded DDF xml-files from the website you indicated but every time I got an err like this:
Will try to contact support.
Thx.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-23 12:05 AM
Sorry JLehr,
I just had to specify the exact model of the equipment and find a specific DDFfile.
The issue is resolved, thank you!